Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

RS485 network problem/no idea

Status
Not open for further replies.

DB_Man

Newbie level 3
Joined
Aug 28, 2008
Messages
4
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,324
rs485 network twisted pair

Hello everyone.

Just started new here cos I'm deperately looking for an answer. Have tried a lot.

Ok, my application first:

PC --> RS232 to RS485 converter --> Digital counter RS485 --> Digital counter RS485 --> Display RS485 --> End of bus.

- All wiring is twisted pair and all devices are the same brand.
- Max length between each device 20m.
- Distance from node to device max 20cm.


I programmed my application in VB 6.0.
What it does:
[*]
<ul>Send request to device 1 - wait - device 1 sends response - read buffer - use response from device 1[/list]
<ul>Send request to device 2 - wait - device 2 sends response - read buffer - use response from device 2[/list]
<ul>Send ASCII string to device 3 for update display[/list]

That happens in a loop.

My application works in a way that I can switch on and off each component individually. Device 1 only. Device 2 only. Device 1 and 2. Update of display separately.

My problem now is that it all works fine on my desk. Once I install it where it is supposed to go the following happens:

I can access device 1 and 2 as long as device 3 is DISconnected from power supply. Once I engergise device 3, d1 and d2 aren't accessible anymore but d3 I can update. ????
I created a simple counter that increases by 1 once I hit a button in my application. That new value is sent to d3 (display). Funny is that occassionaly if I push that button I get a response from d1 or d2. But totally random. Normally I get an update every second.

Already used a different power supply for d3. Nothing.

As I said. My application works perfect without the last device and that distance is only 5 metres from the previous node. Already had the bus terminated (120Ohm) and open. Nothing.

What else can I try?
As I said it works fine on my desk whereas the distances are shorter of the wiring.

Cheers
Sven

PS: Using MSComm for serial connection. Have used different delay times between sending and receiving. RTS signal is switched within program. Works.
 

display rs485

Hi,
So, if this works fine in your desk, and it do not work on the place where it has to be, try finding the cable routes. Are they close to some high voltage cables, that may cause noises trough the communication. That happens very often to me. :)

Best regards,
Julian Dimitrov
 

rs485 network & distances

Already done that.

Used a separate/different connection of twisted pair between d2 and d3 as well as another power supply. Neither helped.

Do you think it could be noise? I mean it works without d3 and d2 and d3 are pretty close together (4m apart).
 

mscomm1 conversor rs485

Hi,
It appears, as a standard, you are using only one power supply for all the three devices; how do you distribute the supply over the distance?

Are you connecting a common ground wire between the devices?

Any possibility of an open in one of the data bus connections at d2? Try interchanging d1 and d2 devices and see if the results are same?

Oserve the bus signal levels and supply voltage with and without d3 being connected.

Switch off all devices and short the bus at d3 and see if short is seen at the PC side only when shorted using a multimeter.

Regards,
Laktronics
 

HI laktronics.
Thanks for your reply.

All three devices have separate power supply (230V AC). So no issues there. I even used another one for d3, just in case. Same result.

I'm not using a common ground for RS485 connection. 2-wire only.

What I did now was, I moved d3 from its position next to d1. Now I can access d1 without problems (delays) and d3 as well. BUT d2 responses only occasionally. Admittedly more often as with previous configuration.

I will try to decrease the baudrate of the bus to see if there is an improvement noticeable.

Do you think a common ground for the bus might help?

Thanks for your help so far.
 

Hi,
Yes, either you use bias resistors or you use common ground, there seems to be a problem with earth connection at D2.

Regards,
Laktronics
 