Continue to Site

Welcome to EDAboard.com

Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Need an indicator light for a 220 water pump

Status
Not open for further replies.

nogero

Newbie level 1
Newbie level 1
Joined
Jul 1, 2013
Messages
1
Helped
0
Reputation
0
Reaction score
0
Trophy points
1
Visit site
Activity points
8
I live in a rural area. I have a 220v submersible water pump. Last summer the pipe broke underground, it was leaking badly and caused my electric bill to go through the roof.

It is a three-wire pump.

Is there an easy way to connect a 110v light fixture to the pump wires so that whenever the pump is running the light is turned on. When the pump is not running the light goes out?
 

I supose you mean under "Three-wire pump" monophase pump.


I suggest to use device for mains socket power metering.

For your original question this can be done many ways, see some examples:

Mains Slave Switcher
**broken link removed**

Instead desklamp you will use wires from water pump.
 

The wires are two 110v hots and a neutral.
They go to the pressure switch where only the hots are routed through the switch contacts when they are closed. The neutral is never switched.
Make SURE the power is off at the breaker and remove the screw to permit the removal of the switch cover. Check the voltage from each wire to ground with a meter, it better read zero otherwise the power is still on and dangerous.
It is now easy enough to put a 4 watt night light bulb between one hot going to the pump and the white neutral. One bulb will tell you when the power is on, which will meet your request.
One bulb on each leg would indicated if there was a problem should only one light. This would suggest a problem with the switch contacts and could lead to premature pump failure.

See digikey.com for other light options. It must be 110v rated. I would stay away from neon indicators since they will become unreliable after 1 to 5 years. There are many panel mount lights with wire leads.

If you are handy a LED, 50k ohm 1/2 watt resistor and a diode with a 600v or greater reverse break down voltage, all in series, will do the job and only consume .13 watts. (It is only on during 1/2 a AC cycle). Drill a small hole in the switch cover for a purchased indicator light or for the LED. Either end of the 3 component string can go to the hot and neutral since you do not care if it is on during the + or - cycle.
 
Last edited:

Status
Not open for further replies.

Part and Inventory Search

Welcome to EDABoard.com

Sponsor

Back
Top