Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

MODBUS response error

Status
Not open for further replies.

bikashh

Full Member level 5
Joined
Nov 28, 2009
Messages
264
Helped
3
Reputation
6
Reaction score
3
Trophy points
1,298
Location
india
Activity points
3,132
hello friends,
I am working in a modbus project...as i am new to this i am not able to figure out the exact problem...

My hardware which is a master is sending request to the MODBUS slave simulator in my PC with the following functions

Slave ID : 0x01
function : 0x03 // read holding registers
Address : 0x0070
Qty :0x001
CRC :xxxx

MASTER REQUEST :01 03 00 70 00 01 85 D1

I am able to send the above request successfully..
but my slave is sending response as

SLAVE RESPONSE 01 83 02 C0 F1


I checked the exception details i.e 0x02
but could not able to understand...


0x02 : Illegal Data Address:

The data address received in the query is not an allowable address for the server (or slave). More specifically, the combination of reference number and transfer length is invalid. For a controller with 100 registers, a request with offset 96 and length 4 would succeed, a request with offset 96 and length 5 will generate exception 02.

the locations i have to read is (0070h - 007Fh) and (0400h - 040F)(as per data sheet from client)

may be i am not able to figure out the exact address...

thanks in advance
 