Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

MGE Pulsar MX 5KVA " No Power Module " detected

Status
Not open for further replies.

poweraces

Member level 3
Member level 3
Joined
Jan 28, 2013
Messages
61
Helped
7
Reputation
14
Reaction score
7
Trophy points
1,288
Visit site
Activity points
1,601
Hi Guys

any one encounter " No Power module" detected on MGE Pulsar MX 5KVA?
UPS in on bypass mode due to this fault.

Any idea how to reset ot to make it On-line? Tnx
 

Are there any alarms on the display, ie No power module then alarm number 703 ?

I would suspect if the unit is already on bypass due to fault, then I would remove and re-seat the power module in the frame and see if any better. Try to restart the Inverter after re-seating the PM
 

Yes there's an alarm number 703.

When i connected to AC source, yes its on bypass mode. i try to remove and reinstall the power module several time but still it detect NO Power Module. I suspect might be the controller board had a problem. But i cant isolate the controller board coz i dont have a spare.
 