Anything goes. Problems you need to be aware of are safe isolation of interlock wiring to power circuits, required noise immunity, possible safety related control requirements.
Most interlock circuits are using normal closed rather than normally open contacts. They are connected in a loop so that any contact opening stops the machine.
Sounds reasonable. Overvoltage protection/current limiting towards the uC would be a good idea, too.It is good when 0.1uF capacitor is added across the connector..?
What is the interlock contact rating?
If it is for small signals like 5V / 100mA then your solution is basically OK.
If it is for high voltage, high current AC ....: then you should consider to use higher voltage combined with higher (swtiching current) maybe use an RC to cause a higher peak switching current. Maybe 24V switching voltage.
The problem with high voltage high current contacts is, that they need this high voltage to keep the contacts free from an oxide at the surface.
Noise:
Not only noise, you also need to protect your microcontroller inputs against ESD. (high speed, high voltage pulses of low energy in both polarities)
--> use proper RC filtering. --> not only a "C" but combined with an "R". With this you are able to get a calculable delay. The delay time should be bigger than the expected noise time constant - including contact bouncing.
Klaus
And it has no contact rating???? and bouncing time...It's mechanical type,there is no electrical operation inside interlock.When the actual value above set value,the contact will close.
tau = R x C10R resistor series with 01.uF is enough for RC filtering..?
tau = R x C
Klaus
Any mechanical switch involves bouncing (10 ms range). Bouncing must not necessarily be a problem in this application, software can filter the signals.
I would however place series resistors to the uC input so that e.g. inadvertently applied 24V control voltage don't damage it. But that's a matter of your device specification.
I've never seen an application that needed an inductor to protect a PIC. A series resistor and maybe a small capacitor to ground should be more than sufficient. If you really are expecting extreme voltages on the interlock connection (very rare) use protection diodes at the PIC pin. I have used interlock wires >10m long in very noisy environments and only used a resistor/capacitor/diode combination and they have never failed in years of operation.
Brian.
Yes: if you expect ESDShall we use ESD protected IC for input sensing..?
An interlock input is a 'go/no-go' logic input and the only real considerations are whether noise can exceed the logic thresholds and how quickly it has to react. Bearing in mind that you have a pull-up resistor to keep the sense line high if the interlock switch is open, the impedance at the PIC is relatively low (1K according to your original post) so it would take a large amount of capacitive or inductive coupled signal to cause any problem. I'm not sure why interlock wiring should be subject to ESD at all but if you want to be absolutely safe, increase the pull-up resistor to say 22K and wire TWO 1K resistors in series with a small Schottky diode (BAT85 or similar) from the junction to ground and another from the junction to VDD. That will let the first (interlock side) resistor absorb any discharges and the second one will further protect the PIC input. If you are worried about high frequency noise, add a capacitor of about 10nF from the PIC input to VSS, it will make a low pass filter in conjunction with the two 1K resistors.
Brian.