Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Distance for drycontact signal ?

Status
Not open for further replies.

khongai

Full Member level 4
Joined
May 20, 2005
Messages
229
Helped
16
Reputation
32
Reaction score
11
Trophy points
1,298
Activity points
2,919
maximum distance for dc signal

Are there any document for the distance of dry contact signals?

As refering to Siemens PLC catalogue, maximum distance of digital input and output are 1000m ( for shielded cable) 600m ( for unshielded cable).

but any information for relay (24VDC) could not be found.

Thank in advance.
 

The maximum distance for the homerun cable depends on:

1) For output, how far below 24VDC can the end device affort?
2) For input, how far below 24VDC can the input card recognize as good signal?

Then you can calcuatel voltage drop to see if the cable is good enough

https://www.stealth316.com/2-wire-resistance.htm



cheers