Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

APC RS-800 overload problem

Status
Not open for further replies.

jamespond

Member level 5
Joined
Mar 11, 2012
Messages
85
Helped
4
Reputation
8
Reaction score
4
Trophy points
1,288
Location
Hungary
Activity points
1,716
I have 3 pieces of RS-800 UPS with same problem. When pressing power button the unit blinks the overload led. If on-line then no charging and after few seconds powering off.
In the unit all fet-s and diodes double checked. 24v, 12v, -12v, 5v is ok!
I searhed for some info, but not find anything. I need some tips or sm for this UPS!

Thank you!
 

if all the FET are ok then you may check the charging circuit of the UPS. there is a chance that it will overload the UPS if the DC voltage is not enough., even you have new batteries.
 

Ok! I will check the charging circuit. I have a new battery.
 