mriksman
Newbie level 5
I was pondering the workings of 4-20mA loops for both inputs (transmitters to a PLC), and outputs (PLC driving an I/P or even a Trip Amplifier).
A loop powered instrument say has a PLC driving a 24V supply to the instrument. Lets say there is 1V drop on the cabling, and the instrument needs a minimum of 12V to run. It then regulates the current to provide the signal back to the PLC. The PLC say has a 250ohm resistor to convert this current to a voltage for measurement; there goes another 5V (20mA * 250ohm). So where does the extra 6V disappear? It just dissipates in the transmitter? Where? Would the transmitter, if I measured across the terminals, show a voltage drop of 18V?
Now I have an analog output. For my pondering it is simply transmitting a 4-20mA to a Trip Amplifier, which on the specifications says has a 5ohm input impedance (the device is a RTK P607). I have measured the voltage with the Trip Amplifier disconnected, so the wires are simply connected to the PLC. I am reading 22.5V. I presume the losses are due to the wiring. OK, so the PLC has a 24V output signal, and can drive a 4-20mA signal. Well, at 20mA, where is the voltage dropped? If connected to the Trip Amplifier, wouldn't there be a drop of 0.1V? (20mA * 5ohm)? Where is the rest of the voltage dropped?
I'd like someone to tell me if I had my voltmeter - where I would find each and how much voltage drops at what location.
Oh, and a side question. The 'senior' guy said to me, 'you can measure the current on the analog output wires using an ammeter because it is high impedance'. Ummm, isn't the ammeter a low impedance device? Essentially a dead short? I didn't check, but I can only surmise the current whizzed through the ammeter, and none went on to the Trip Amplifier at that point. If the Trip Amplifier had actually have been in operation with a low trip point, I can only guess it would have tripped the pump!!
Thanks for any information.
Mike
Mike