1-10A doesn't sound plausible, for an AC CT, that is basically a linear passive device (not considering possibe saturation. It can measure 0 current as well.I've been searching for 0-10A range but only manage to find 1-10A
Correct according to ohms law, but possibly not permitted by the CT specification, that e.g. requires a shunt below 50 ohm.you need 5V output, then r=V/I= 5V/28.214mA = 176.78 ohms
so your current is 10A that is RMS value. then your peakcurrent is 10*sqrt(2) = 14.142 A ;
with this let us come to design part;
suppose you have 1:500 current transformer(CT) then the secondary current is 14.142/500 =28.284mA (peak);
you need 5V output, then r=V/I= 5V/28.214mA = 176.78 ohms, so you put this resistor in secondary, this set up gives 5V(AC Peak) across resistor for 10A input, then use any precision(active) rectifier. this rectifier output gives 0VDC to 5VDC for 0A to 10A.
The above is true only if the measured current is sinusiodal and your precision rectifier is also a peak rectifier, there will need to be a decay on this, so the time taken to read currents accurately as they fall may be several 10's of cycles. If your ADC can handle bipolar signals then no need for an op-amp rectifier, but you may want to sample several times over an half cycle to get an accurate actual end reading, or sample in synch with the peak of the mains.