Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

What will happen if I touch the chassis and there is no connection to ground?

Status
Not open for further replies.

iVenky

Advanced Member level 2
Joined
Jul 11, 2011
Messages
584
Helped
37
Reputation
76
Reaction score
35
Trophy points
1,318
Location
College Station, Texas
Activity points
6,124
I got one doubt. I read that chassis is the return path for the current in any equipment. So it means that there is greater amount of exposure to current in chassis. So if I touch the chassis and there is no connection to earth then what will happen? :|
 

Hello,

The chassis (equipment with PE, that is three terminal plug) is used for return current if a failure occurs (live wire connects to the chassis). The current flows back via the PE (protective earth) wire that is connected to the chassis. The fuse or residual current switch activates in case of faillure. If PE is not present in such case, there may be live voltage on the chassis (can be lethal).

The chassis is also the return current for the so-called Y interference supression capacitors. These capacitors are between the phases (or phase and neutral) and the chassis.

when you connect a device that requries protective earth to a socket without protective earth, and you touch it, current may flow through the Y capacitor(s) to the chassis and from the chassis through your own body to ground.

Consumer equipment has a limitation on the earth leakage current so that the shock will not be directly lethal, if there is an earth fault. However equipment for industrial use may have leakage current via the Y capacitors that can be above 3.5 mA. Such equipment may be used only with fixed wires and may require two earth paths to enhance safety.

Generally spoken, equipment that is equiped with PE should be used on a socket with PE only (I know that this isn't done always). The reason is that the strength of insulation in equipment with PE requirement is less then for equipment without PE requirement (such equipment requires double or reinforced insulation).
 