Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

What is the length of the wire for the following problem?

Status
Not open for further replies.

iVenky

Advanced Member level 2
Joined
Jul 11, 2011
Messages
584
Helped
37
Reputation
76
Reaction score
35
Trophy points
1,318
Location
College Station, Texas
Activity points
6,124
Here's the question:

A twin- core cable is used to supply a 1kW load. The supply voltage is 100 V ac. The regulations state that the voltage at the load should be within 5% of the supply voltage. Determine the maximum length of cable run that therefore can be used. The resistance of the cable is 6.28 * 10-8 Ω/m and the cross section area of the cable is 1.57 mm^2.


Thanks in advance.:grin:
 

Uin=100V,
P = U I = 1000W -> I = 10 A


U load = 95% Uin=95V
U cable = 5V
but
U cable = I * R cable
R cable = U cable/I = 5/10 = 0.5Ω
R cable = 2 Rwires

Rwires = ρ * l / A

A = 1.57 mm2 =1.57 * 10 -6 m2
ρ =6.28 * 10-8 Ω/m
R wires = 6.28 * 10-8 * l / 1.57 * 10 -6 = 4.331 * 10 -2 * l
R cable/2 = R wires = 4.331 * 10 -2 * l
R cable = 2* 4.331 * 10 -2 * l = 0.5
l = 0.5/(2* 4.331 * 10 -2) = 50/8. 662 = 5.77 m
 