I've been trying to resolve an issue with a pump controller project where the customer needs a long run time (5 minutes) and this time length generates too much heat on the control triac. Currently the triac is PCB mounted; the board doesn't provide enough heat sink space, and a separate heat sink cannot be too big as space is limited.
I had this idea of using a triac / relay combination to reduce the heat in which they would be connected in parallel. The triac would turn on first, then 1 second later the relay would close. This would drop the voltage across the triac to almost nothing and the heat would go away. At turn off, the relay would open first and with the triac still on and pulling current, there should be no arcing since the triac drop is only 1 volt.
So... no relay contacts arcing and no triac heat build up.
Any real drawbacks on this? It seems like a really ingenious solution here, so I'm wondering what else I need to consider.
One thing though is the contact ratings. Since the relay will not ever switch the full line voltage (120 VAC), can I get away with using a relay with 12V contacts? I'm looking at some small ones for about $3 with 10A contacts.
Thanks for any input.
I had this idea of using a triac / relay combination to reduce the heat in which they would be connected in parallel. The triac would turn on first, then 1 second later the relay would close. This would drop the voltage across the triac to almost nothing and the heat would go away. At turn off, the relay would open first and with the triac still on and pulling current, there should be no arcing since the triac drop is only 1 volt.
So... no relay contacts arcing and no triac heat build up.
Any real drawbacks on this? It seems like a really ingenious solution here, so I'm wondering what else I need to consider.
One thing though is the contact ratings. Since the relay will not ever switch the full line voltage (120 VAC), can I get away with using a relay with 12V contacts? I'm looking at some small ones for about $3 with 10A contacts.
Thanks for any input.