Siemens 3RT1045-1AP00

Status
Not open for further replies.

rikotech8

Member level 1
Joined
Apr 22, 2012
Messages
36
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,286
Activity points
1,591
https://www.google.bg/url?sa=t&rct=j&q=&esrc=s&frm=1&source=web&cd=1&cad=rja&uact=8&ved=0CD8QFjAA&url=http%3A%2F%2Fwww.slo.lt%2Fout%2Fmedia%2F3RT10451AP00_en.pdf&ei=Ur15U4aDMsim0AWxgoDADw&usg=AFQjCNG8KcMdESWBzSwH294UJKG6badiDQ&sig2=DrpMHLrLVbQdYFJSS_JU2g&bvm=bv.66917471,d.bGQ

Hello everyone!
The link avove points to a contactor switch datasheet. That contactor is used in my house instalation. The question came accross is: Looking at the datasheet table, there is control circuit section. What this data mean?: Operating range factor control supply voltage rated value / ofthe magnet coil 0.8 … 1.1.
https://drive.google.com/file/d/0B_EYtdS7J5eKQXJsYUpxanU3MDQ/edit?usp=sharing

So again what means that range? If someone can describe that parameter little bit more, I would much appreciate that?
Thank you in advance!
 

control voltage range 0.8 ... 1.1 says the contactor will be safely engaged with a coil voltage > 184 VAC. The coil shouldn't be exposed to a voltage above 253 VAC to prevent overheating.
 

Thank you for your prompt reply!
I tought so too. What confused me is, that I anticipated real numbers (what you showed me) rather than relative range (0.8 - 1.1)*rated_voltage. Anyway, thank you again.
 

Status
Not open for further replies.
Cookies are required to use this site. You must accept them to continue using the site. Learn more…