Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Multiplexing RS 232 signals and RS485 signals for BMS

Status
Not open for further replies.

kalidas nadar

Newbie level 2
Newbie level 2
Joined
Sep 7, 2013
Messages
2
Helped
0
Reputation
0
Reaction score
0
Trophy points
1
Visit site
Activity points
15
Hi Amigos,
I am new to this forum & i need ur much appreciated help for BMS connection .
I am getting RS232 signal from Turbocor I/O Board and RS485 signal from Carel PCO3 controller .
I want to connect both these signals to modscan software. Unique device ID(address) will differentiate both of them in modscan software . I have tried converting RS232 signal to RS485 signal and then connecting that in parallel with the RS485 signal which i am getting from PCO3 controller but to no avail :?: . In modscan i was able to detect only signals from PCO3 controller but not from the converted signal from Turbocor I/O board . Also suggest me link to some good RS232 to RS 485 converter .

Thanks & Regards,
dor4 ;-)
 

Hi Amigos,
I am new to this forum & i need ur much appreciated help for BMS connection .
I am getting RS232 signal from Turbocor I/O Board and RS485 signal from Carel PCO3 controller .
I want to connect both these signals to modscan software. Unique device ID(address) will differentiate both of them in modscan software . I have tried converting RS232 signal to RS485 signal and then connecting that in parallel with the RS485 signal which i am getting from PCO3 controller but to no avail :?: . In modscan i was able to detect only signals from PCO3 controller but not from the converted signal from Turbocor I/O board . Also suggest me link to some good RS232 to RS 485 converter .

Thanks & Regards,
dor4 ;-)

first of all rs232 is full duplex , while rs485 is half , so it is not direct conversion.
use max232 to convert rs232 to ttl , then use max485 to convert rs485 to ttl , but u will a need a control signal for max485 to choose if u are in recieve or transmit mode . or use can use pull up or pull down if u have only one way communication ..

hope that helps
regards
 