Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

[SOLVED] Masterguard series E 80-3

Status
Not open for further replies.

zumaianh

Newbie level 3
Joined
Aug 19, 2013
Messages
4
Helped
0
Reputation
0
Reaction score
0
Trophy points
1
Activity points
23
UPS E 80-3 No power

Hello,
I have a Masterguard UPS E 80-3 . It could not start. I checked the fuse found ok.
1. i am looking for the manual of it.
2. I need possible problem that could not start the system.




Please HELP.
Thank you
 
Last edited:

check battery supply it should be proper voltage. if not then change battery/ check ouput side mosfets/ check battery series
conected fuse



if found usefull then press helped me button
 
I have disconnect the batteries from the system.
and apply 460 voltage 3 phase + N + G.
i understand at least the system should be on, but the equipment looks dead.
 

thank you i will check it again.
i am not sure about batteries voltage. i have to check it again.
 

I found 20 batteries the total reading 26 while they should have reading from 220 to 240 vdc as per battery data.

Seal Battery
12 VDC
26 AH
 

then you have to charge the each battery using battery charger, if charging fails then you have to replace the bateries
 