Continue to Site

Welcome to EDAboard.com

Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Generator field control

Status
Not open for further replies.

btahir90

Junior Member level 2
Junior Member level 2
Joined
May 27, 2012
Messages
22
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Visit site
Activity points
1,457
I am working on a project which is Automatic voltage regulator of fenerator using field contol through PWM

problem is what should be the frequency of PWM

generator draws 1 A at 50v dc field at full load and 0.5 A 19 v at no load.

my idea is to choose a mosfet and a diode to prevent transients. pwm directly from microcontroller. would it work?
 

What are the specifications of the motor you are using?

my idea is to choose a mosfet and a diode to prevent transients.

where is your circuit?
 

its not a motor its an alternator of 2.5kw . i need to control its terminal voltage with field current.

- - - Updated - - -

here is cicuit diagram
mosfet using is IRF740
frequency to choose is 1kHz.
 

Attachments

  • PWM circuit.jpg
    PWM circuit.jpg
    20.9 KB · Views: 123

Is the circuit working?
your pwm frequency should be optimum where losses would be low
 

Status
Not open for further replies.

Part and Inventory Search

Welcome to EDABoard.com

Sponsor

Back
Top