Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

current limiter for 230v

Status
Not open for further replies.

ravni

Newbie level 1
Joined
Jul 31, 2013
Messages
1
Helped
0
Reputation
0
Reaction score
0
Trophy points
1
Activity points
10
Hi. I have a 2300watt water heater element. Is there a relatively easy methode to control the amount of power I'm putting into it? So that I can use it as a etc. 1000watt element..
 

The simplest one is a dimmer using diac & triac. But it is not a recommended solution since it generates high interference on the power line. So using it depends on your location and if there are or not sensitive sets connected also to the power line.
 

If you have two 1-kW heaters, you can connect both series and get 500 W heat output. With one alone, you get 1 kW. With both in parallel, you get 2 kW. So with a simple switch you can get three levels, simply and without electronics and interference.
 

A more complex solution is by using a continuous on-off timer with a period of a few minutes for example.
The idea is to turn on (and off) the heater's current for an interger number of mains cycles (at voltage zero crossings).
 

To implement KerimF's suggestion, you can use a solid-state, zero-crossing relay to control the heater.

A few minutes ON may be too long, depending upon the thermal time-constant. You may want the ON/OFF period to be in seconds or even fractions of a second. You could use a 555 configured as a variable (PWM) astable multivibrator to control the ON/OFF duty-cycle.
 