Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Where should be the load current is checked - At motor end, at output of drive (VFD /

Status
Not open for further replies.

dineshdeshmuk

Full Member level 5
Joined
Sep 12, 2011
Messages
285
Helped
18
Reputation
36
Reaction score
18
Trophy points
1,298
Activity points
3,131
Where should be the load current is checked - At motor end, at output of drive (VFD / Inverter) or at incomer to the drive (input supply to the drive) ?

In a set-up where motor is connected with the VFD to control its speed, its frequency etc.
 

you have two loads in effect, So the first is the input to the VFD, this takes MORE power then the load (load power + losses). The second is the motor. So you might have 230 @ 40A going into a VFD and 415 V three phase at 6A/phase coming out.
Frank
 

to check that a motor is taking how many amps , where should connect the clamp meter to check the amps ?

at the motor, don't you think that there would be distorted output which would change the reading
 

to check that a motor is taking how many amps , where should connect the clamp meter to check the amps ?

at the motor, don't you think that there would be distorted output which would change the reading

VFD's output voltage is PWM sinewave, but the output current gets real sinewave due to the motor's inductance. So there is no problem to measure current at the motor. Measuring current at the motor (VFD's output) using clamp meter is a common practice.
 