Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Whats the Differenece b/w PLC and DCS

Status
Not open for further replies.

ayyub

Newbie level 6
Joined
Jul 11, 2008
Messages
14
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,384
plc vs dcs

Hi Friends!
I want to know that what is the basic difference between a PLC and a Distributed Control System.I want some detail data on this with figures because i got my final Presentation on Distributed Control System.So my presentation would be more effective if you guyz guide me.Thanks
 

plc dcs forum

You have hit upon a discussion that has been raging in the industry for 20-30 years. Over the years, the two have come together to the point that there is not a whole lot of difference. The biggest difference is probably in their origins.

PLC's originated with discrete control. Designed to replace large amounts of relays. This also is the reason for PLC's dominant programming language being ladder logic. The target audience was electrical engineers and electricians. Ladder logic is well suited to the core training of both disciplines so EE's and electricians can understand ladder programs due to their similarity to electrical ladder diagrams. Over the years the functionality required by advanced ladder programs has somewhat negated this advantage. Many of the commands available are in no way comparable to electrical components. PLC's have also expanded to include structured text programming, function block programming and step programming. Analog I/O and capabilities have been developed to cover a full spectrum of possibilities. SCADA systems have developed to be paired with PLC's to allow full visualization and data manipulation.

DCS's originated to fill in with analog control. Developed for process industries, they were designed around process engineers - usually chemical engineers. They were designed for large systems and generally were programmed with some form of high level language or function block programming. They now have ladder and discrete functionality and even tend to look more like the PLC's. DCS's tend to integrate the visualization and data manipulation better than their PLC counterparts as their configuration is usually a single system designed to work as a whole; however, the PLC manufacturers have made strides into duplicating this capability. The costs of DCS systems are generally higher than comparable PLC systems.

I really dont see a lot of difference today between the two platforms. EE's tend to gravitate toward the PLC's still and Chem E's tend to still gravitate towards the DCS's. The PLC manufacturers are constantly trying to break the image of small system and/or discrete machine control even after all these years. Many of them have gone to calling their upper end controllers PAC's or programmable automation controllers. Change the name lose the stigma.

Hope this helps
 