Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

What is the function of Motor in the motorized circuit breakers?

Status
Not open for further replies.
"motorized" circuit breakers use the motors to re-charge the mechanical springs that actually perform the moving of the contacts. The motors are often 50 V battery supported, so they can be operated when there is no mains available.
Motorized circuit breakers are used on high power circuits, we had them on a 11KV incoming supply that fed a 1MW 440V transformer. The actual trip was a 50V coil circuit, so passing 50 mA current through the trip circuit, caused the switch to open (on the springs) and break the 1 MW circuit. So the earth leakage would only be one of several things that fired the switch (over current, loss of a phase. . . )
Frank
 