Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Variable autotransformer pri and sec resistance

treez

Advanced Member level 5
Joined
Sep 22, 2008
Messages
7,898
Helped
578
Reputation
1,159
Reaction score
557
Trophy points
1,393
Location
cambridge
Activity points
78,147
Hi,
Do you know pri and sec resistance of this?
We wish to run with a 480VA load, but wish to see how close to 270VAC we can get on max load.
(With an input of 240VAC)

>>>>>>>>>>>>>>>>>
Same question but with this one...

Our mains input current looks as follows
 
Last edited:

treez

Advanced Member level 5
Joined
Sep 22, 2008
Messages
7,898
Helped
578
Reputation
1,159
Reaction score
557
Trophy points
1,393
Location
cambridge
Activity points
78,147
Hi,
Does anyone know of the datasheet for the well known Clairtronic Mains autotransformer?

It has no part number on it, just a hand written Type number of "10555". And a hand-written serial number of "360/022006"
I believe many will know the one that i mean, as this particular one is massively common in many electronics co's that i have been to. It has a light grey paint work on its cylindrical type enclosure, with black dial on top so you can rotate it to your desired voltage.
All else it says on it is 240VAC in, 0-240VAC out, and a little split coil diagram with connections 1,3 and 5. The dial markings go from "0" to "270". From the coil diagram, its obvious that Vac input is always >= VAC output.
I am trying to find out the coil resistance. Officially. I am not allowed to take it too much apart. I took off the cover which covers the input/output lead entrance points, and measured the primary and secondary resistances with the wiper at max......so the readings should have been the same, but were not....
The primary resistance was 0.8R. However, the secondary resistance came out as 2.3R, so i am guessing the wiper is making up the deficit in resistance. Presumably this means its damaged?
Does anyone have the datasheet?
 

FvM

Super Moderator
Staff member
Joined
Jan 22, 2008
Messages
48,285
Helped
14,228
Reputation
28,717
Reaction score
12,923
Trophy points
1,393
Location
Bochum, Germany
Activity points
279,606
How do you measure primary and secondary resistance of your autotransformer? Do you understand which winding resistances form the effective transformer output impedance?
 

c_mitra

Advanced Member level 5
Joined
Nov 13, 2012
Messages
3,612
Helped
905
Reputation
1,812
Reaction score
873
Trophy points
1,393
Activity points
28,231
The resistances to be measured between the two end points. B. ut you can also measure the resistances between the two ends and the wiper.

What is actually need to measure, and that is a difficult task, is the impedance of the winding. It is difficult because it varies with the load (current) and the wiper position (voltage output).

For all practical purposes, model it as a "regular" transformer with the primary and secondary in series. Adjust input and output as per taste.

When everything fails, just simulate.

But frankly I am puzzled to see the primary resistance to be 0.8R and the secondary resistance to be 2.3R. Getting curiouser and curiouser. Turn the dial and measure it again.
 

BradtheRad

Super Moderator
Staff member
Joined
Apr 1, 2011
Messages
14,001
Helped
2,789
Reputation
5,576
Reaction score
2,696
Trophy points
1,393
Location
Minneapolis, Minnesota, USA
Activity points
104,435
I own three autotransformers. Here's the 3000W unit. Bidirectional, fixed ratio, 120V-240V. I measured ohmic resistance using my DMM on the lowest range. Every reading was under 1 ohm. I tested between taps and commons, red, black, all.
0412211810.jpg
 

dick_freebird

Advanced Member level 5
Joined
Mar 4, 2008
Messages
7,232
Helped
2,117
Reputation
4,238
Reaction score
1,968
Trophy points
1,393
Location
USA
Activity points
57,987
It occurs to me that you might be better off with
a plurality of different-ratio transformers, than
a Variac. For one, you'd get isolation. For another,
as much copper and iron as you like, at cheapest.
Surplus, even. Rather than fiddling about on the
Web, buy a brace of fat isolation xfmrs and start
removing primary windings, in a series that nets
you a "good enough" step resolution for whatever
experiment you think you're going to do.

Sure, it's select-plug rather than "turn the knob".
You could probably step through smartly if you
had a high power contactor matrix under logic
control.
 