1.1.1 Voltage Magnitude Synchronizing Variable
If the voltage magnitudes are not closely matched, a sudden rise in Mvar flow will appear across the circuit breaker as it is closed. For example, if a 345 kV circuit breaker were closed with a 20 kV difference in voltage across the open circuit breaker, a large Mvar flow would suddenly occur upon closing. The allowable voltage magnitude differences across the open circuit breaker are system specific. However, for general guidance, a difference of a few percent is unlikely to cause any serious problem.