Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Transformer in parallel? (urgent)

Status
Not open for further replies.

khongai

Full Member level 4
Joined
May 20, 2005
Messages
229
Helped
16
Reputation
32
Reaction score
11
Trophy points
1,298
Activity points
2,919
Can i connect 2 transformer (24kV/.4kV - 2000kVA) to one busway of LVSG.
thank in advance.
 

Transformers can be banked in parallel to multiply capacity but you need to make sure that
1) impedance ratio is identical
2) their voltage ratings are the same (including tap settings)
3) polarity is correct
4) proper switchgear is used on both side of the transformer.

Even a small mismatch will create HUGE current loops.
In short yes, but get it done by specialists.

Added after 4 minutes:

I forgot to mention
5) make sure that your busses can handle the increased current flow
6) make sure your earthing can handle the increased prospective ground fault currents.

Which still says - get it done by specialists.
 

hi
7) special protection (REF, directional OC ,synchro check relay) must be added.
8) To have safe operation same interlock have to considered .
 