you don´t have a 1kV transformer --> you have a 1kVA transformer.
***
To your question:
Current:
If a transformer winding is rated for 10A, then you NEVER should draw 20A continous RMS current.
Maybe you could overload it for a short time...
Twice the RMS current will cause 4 times power dissipation and thus 4 times temperature rise.
***
Voltage: you say 50V:
How do you think you could get 50V from a 100V output?