Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Too many Y caps means tripped RCD?

cupoftea

Full Member level 5
Joined
Jun 13, 2021
Messages
281
Helped
5
Reputation
10
Reaction score
10
Trophy points
18
Activity points
1,724
Hi,
if i plug in loads of mains devices which contain Y caps from live/Neutral to earth, then at some point the RCD will trip?
 

betwixt

Super Moderator
Staff member
Joined
Jul 4, 2009
Messages
15,127
Helped
4,935
Reputation
9,890
Reaction score
4,742
Trophy points
1,393
Location
Aberdyfi, West Wales, UK
Activity points
128,440
A rough calculation says the value should be less than 0.8uF, assuming the capacitor and RCD are in series and directly across 240V 50Hz. I would expect it to be a little higher when other filter impedances are also present.

Brian.
 

KlausST

Super Moderator
Staff member
Joined
Apr 17, 2014
Messages
20,356
Helped
4,441
Reputation
8,891
Reaction score
4,468
Trophy points
1,393
Activity points
134,577
Hi,

It surely depends on RCD trip current.

Klaus
 

cupoftea

Full Member level 5
Joined
Jun 13, 2021
Messages
281
Helped
5
Reputation
10
Reaction score
10
Trophy points
18
Activity points
1,724
Also, its the y cap between live and earth that gives the most current to earth........the one across the transformer isolation barrier gives much less, and the y cap from neutral to earth gives virtually nothing.
The Y cap across the transformer, especially if sec gnd is earthed, actually gives a noisy current shape..."sharp cornered"...probably no good for emc...what do you say?
 

cupoftea

Full Member level 5
Joined
Jun 13, 2021
Messages
281
Helped
5
Reputation
10
Reaction score
10
Trophy points
18
Activity points
1,724
If you run the attached simulation of a rep of an offline SMPS with three 2n2 Y capacitors, then you can see that theres only actually 261uA of earth current from 240VAC input.
The Y cap from neutral to earth contributes nothing, and the Y cap across the transformer contributes less than the one from live to earth....the striking thing is that due to the secondary being earthed, the y cap across the transformer actually has a sharp current waveform, which woudlnt be good for emc.

If common mode inductance is added, then it gats worse, as the cap across the isolation barrier...well, it then puts a ringing current into earth...which is bad for conducted EMC...so i see the cap across the isolation barrier comes with disadvantages.
 

Attachments

  • Y cap current in earth.jpg
    Y cap current in earth.jpg
    80.3 KB · Views: 28
  • RCD TRIP FROM Y CAP CURRENT.zip
    1.1 KB · Views: 2
Last edited:

FvM

Super Moderator
Staff member
Joined
Jan 22, 2008
Messages
48,755
Helped
14,307
Reputation
28,877
Reaction score
13,035
Trophy points
1,393
Location
Bochum, Germany
Activity points
281,570
How can we relate post #5 and #6 to the original question? RCD trip current is at least in a several mA range, it can't be achieved by nF Y capacitors.
 

c_mitra

Advanced Member level 5
Joined
Nov 13, 2012
Messages
3,740
Helped
921
Reputation
1,844
Reaction score
907
Trophy points
1,393
Activity points
29,399
How can we relate post #5 and #6 to the original question? RCD trip current is at least in a several mA range, it can't be achieved by nF Y capacitors.
Right; also several mA (I guess 10mA at the peak is closer to reality) should be maintained during at least one 1/2 cycle. In my guess, it is the total energy that matters in the tripping (delivered over 10-20ms).
 

KlausST

Super Moderator
Staff member
Joined
Apr 17, 2014
Messages
20,356
Helped
4,441
Reputation
8,891
Reaction score
4,468
Trophy points
1,393
Activity points
134,577
Hi,
In my guess, it is the total energy that matters in the tripping (delivered over 10-20ms).
If so, then a purely capacitive current means "no energy". Then an RCD never trips with capacitive current.
I doubt this ... although I don't know for sure.

Klaus
 

c_mitra

Advanced Member level 5
Joined
Nov 13, 2012
Messages
3,740
Helped
921
Reputation
1,844
Reaction score
907
Trophy points
1,393
Activity points
29,399
then a purely capacitive current means "no energy". Then an RCD never trips with capacitive current.
I doubt this ... although I don't know for sure.

A purely capacitive current in the capacitor really means "no energy" but when you make the same current flow through a resistor or a transformer primary, strange things can happen. This current is 90 deg out of phase with the voltage only across the capacitor, if my understanding is not rusted.

RCD detects the unbalanced current via a transformer and the trip mechanism is a load on this transformer. All mechanical relays cause a change in the magnetic flux during closing on/off period and the magnetic energy is transferred to the spring of the relay contact (mechanical energy).

Do correct me if I am talking nonsense.
 

KlausST

Super Moderator
Staff member
Joined
Apr 17, 2014
Messages
20,356
Helped
4,441
Reputation
8,891
Reaction score
4,468
Trophy points
1,393
Activity points
134,577
Hi,

I think there is a misunderstanding.

My thinking was the "external energy" or the "load side energy".... like an energy meter does.
Your thinking is some kind of RCD internal energy.

To avoid this confusion let´s go back to RCD trip point definition:
Here in Germany the trip point is defined as "current RMS". Like "30mA".
And I assume this trip point does not care about phase shift related to phase voltage. So it´s a pure current related trip point.
And it also does not care about RCD internal resistor´s (or other circuitry) power loss or energy. I think the RCD internal power loss may be different from brand to brand .. even with identical trip current.

Klaus
 

c_mitra

Advanced Member level 5
Joined
Nov 13, 2012
Messages
3,740
Helped
921
Reputation
1,844
Reaction score
907
Trophy points
1,393
Activity points
29,399
To avoid this confusion let´s go back to RCD trip point definition:
Here in Germany the trip point is defined as "current RMS". Like "30mA".
I am trying the say the same thing.

The 30mA trip current must be associated with a time spec; I assume this should be at least a quarter period or more likely a half cycle (else the RMS definition becomes problematic).

I also assume that the frequency should be around 50Hz (domestic frequency) that means that the 30mA current must last at least 5ms or preferably 10ms.

My point is that the trip switch needs some energy to turn on/off. Why?

Consider the gedanken. Assume you have a good FET switch that can be turned on or off with a single pulse.

How much energy the FET needs to turn on or off? That depends on the junction capacitance and the turn on voltage.

You cannot have a FET that have ZERO junction capacitance and also turns on at a very low voltage. And it also depends on the power you are switching on or off.

Consider a bistable switch state. The pulse must deliver some power to the circuit to turn it on or off.

Same idea goes for a mechanical relay.

When the current changes from 0-30mA, the RCD trips. Will the RCD trip if the current pulse is 1ms wide? My answer is no; the pulse must supply some energy to trip the mechanism and that is some finite energy.

How about a circuit in which a small and sensitive relay trips a bigger relay and that in turns turns a still bigger one?
 

KlausST

Super Moderator
Staff member
Joined
Apr 17, 2014
Messages
20,356
Helped
4,441
Reputation
8,891
Reaction score
4,468
Trophy points
1,393
Activity points
134,577
Hi,

I agree that there needs to be a trip time specified.

I´ve done an internet search. In one document I found it says:
200 ms with 1x I_deltaN
40ms with 5x I_deltaN
Don´t know wheter this is a common specification.

the RCD is manually switched on ... the energy to switch OFF is stored in a spring.
And the trip current just needs to release the spring energy.
(Very small energy to release ... compared to the spring energy)

Klaus
 

c_mitra

Advanced Member level 5
Joined
Nov 13, 2012
Messages
3,740
Helped
921
Reputation
1,844
Reaction score
907
Trophy points
1,393
Activity points
29,399
the RCD is manually switched on ... the energy to switch OFF is stored in a spring.
And the trip current just needs to release the spring energy.
(Very small energy to release ... compared to the spring energy)
True; but.

When you turn on the switch, you need to push the spring against a peak. The switch spring settles in the on position which is a potential energy valley on the other side. The on position of the spring is a potential energy valley which is much higher in energy compared to the off position. To turn off the switch, you need to push the lever across the peak (which is small but must be much greater than the noise threshold) and after this level is crossed, the manual lever disengages and the mechanism turns off. This is to prevent (rather reduce arcing) the contacts from getting damaged.

But this is very clear that the few uAs of current flowing through Y-capacitors for less than a millisecond cannot trip a RCD even if 1000 such devices are turned on exactly at the same time.

Gas centrifuges used for isotope separations are run by individual power supplies and they must not be turned on at the same time and there are 10,000 (or more) of them running in series with in one place. And they run hours and days and months continuously at a time. And they can be replaced individually without stopping the whole setup.
 

Easy peasy

Advanced Member level 5
Joined
Aug 15, 2015
Messages
3,337
Helped
1,168
Reputation
2,336
Reaction score
1,251
Trophy points
113
Location
Melbourne
Activity points
18,110
a repair place next door has no end of issues with RCD tripping due to > 10nF Y caps on 3 ph chargers, 10mA RCD, always trips at turn on ....

chop out the Y caps - no issues ....
 

c_mitra

Advanced Member level 5
Joined
Nov 13, 2012
Messages
3,740
Helped
921
Reputation
1,844
Reaction score
907
Trophy points
1,393
Activity points
29,399
A rough calculation says the value should be less than 0.8uF,
Surely you mean more than 0.8uF? My estimate is in the same range, it must be greater than 0.47uF across the line and earth (net unbalanced)
 

betwixt

Super Moderator
Staff member
Joined
Jul 4, 2009
Messages
15,127
Helped
4,935
Reputation
9,890
Reaction score
4,742
Trophy points
1,393
Location
Aberdyfi, West Wales, UK
Activity points
128,440
sorry, misunderstanding, I meant if the the value is more than 0.8uF there is a risk of a standard 30mA RCD tripping. As most 'Y' capacitors are only a few nF it would take lots of equipment containing them to cause a false tripping condition. By the time enough capacitor current had operated the RCD, the chances are the overload breaker would already have operated.

Brian.
 