Regd Networking of 8 nodes using CAN

Status
Not open for further replies.

Srikrishna

Newbie level 4
Joined
May 20, 2011
Messages
5
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,319
Hi

I want to network 8 nodes through Controller Area Network.

The CAN protocol says that the connection should be like..a single bus to which all the nodes are connected.

So does that mean that the connecction should be like in fig (1) of the image shown.....or can it also be like in (2).....


---------- Post added at 15:51 ---------- Previous post was at 15:49 ----------

I mean...the CAN protocol saying that...a single bus to which all the nodes are connected..is it just a way of visualizing it..or is it that even physically the connection is like that??
 

logically (and sometimes physically) it is fig 1 - the stations are multidropped of the bus with a terminator at each end.
physically is can be wired like fig 2 with a pair of sockets with the CANL and CANH lines of the sockets connected on the PCB - so the final wireing is like fig 1
 