Welcome to our site! EDAboard.com is an international Electronic Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Register Log in

Loss of Neutral can cause damage to mains conencted devices...how avoid damage?

Z

zenerbjt

Guest
Hi,
As you know, all electricity from your national grid is ultimately three phase in origin. If the neutral gets disconnected somewhere in the supply, then the Line-Neutral voltage becomes the Line-Line voltage, and any connected devices may well get overvoltaged and blow up.

For a 10kW installation, supplied with three phase, how can we ensure that the Line-Neutral voltage does not rise up to the line-line voltage if there is a loss of neutral connection?
 

KlausST

Super Moderator
Staff member
Joined
Apr 17, 2014
Messages
18,761
Helped
4,184
Reputation
8,370
Reaction score
4,120
Trophy points
113
Activity points
123,389
Hi,

Not clear how the setup is.
Do a simulation and show us the results.

Klaus
 
  • Like
Reactions: zenerbjt

    Z

    points: 2
    Helpful Answer Positive Rating

betwixt

Super Moderator
Staff member
Joined
Jul 4, 2009
Messages
14,591
Helped
4,782
Reputation
9,581
Reaction score
4,562
Trophy points
1,393
Location
Aberdyfi, West Wales, UK
Activity points
124,351
This actually happened near my home a few years ago. I'm in a very rural location with ancient and unreliable power distribution. Our electricity arrives as true three phase (only three wires) 11.5KV then gets dropped to 240V TP&N at the transformer which then heads off along four core cables to several small distribution boxes. Each of the small boxes feeds between four and six properties as single phase plus neutral.

The incoming neutral wire corroded and burned out at one of the distribution boxes, leaving six houses sitting across the phases. I was called out to investigate and called at one of the houses. It was quite funny in a tragic kind of way, the owner showed how they could switch their electric kettle on and make the lights in the house across the road turn on instead!

Thankfully there wasn't much damage and repairing the neutral restored some normality. Other than big varistors across the supply to protect each phase there isn't much you can do. At least its an obvious fault when you see the symptoms.

Brian.
 

FvM

Super Moderator
Staff member
Joined
Jan 22, 2008
Messages
47,872
Helped
14,125
Reputation
28,507
Reaction score
12,808
Trophy points
1,393
Location
Bochum, Germany
Activity points
277,837
Varistors aren't selective enough to protect in this situation. You can install overvoltage circuit breakers in the switchboard.
 

Easy peasy

Advanced Member level 5
Joined
Aug 15, 2015
Messages
2,794
Helped
1,008
Reputation
2,016
Reaction score
1,024
Trophy points
113
Location
Melbourne
Activity points
15,565
You can install a transformer in your home that is designed to provide and augment the neutral - unfortunately it will do the same for anyone on the same 3ph + N supply, best bet is some very large MOV's from each phase to N, and a trip circuit - or fuses - that will disconnect the mains if significant current ever flows in the MOV's
 