Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Automatic AC Bulb Fuse Detection Circuit

Status
Not open for further replies.

Jahanzeb1

Newbie level 6
Joined
Mar 29, 2012
Messages
11
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,399
Hello !

I have an AC bulb operating at 220v 50Hz , i want a circuit that determines automatically either the bulb is fused or not. I need 5v and 0v logic for this purpose as i need this feedback for the micro-controller.

I have considered several solutions for this purpose :

1. When the bulb is fused circuit becomes open so we can add a current sensing op-amp circuit in the path.
2. Convert the AC to DC without transformer configuration and make 5v DC from 220v AC and directly give it to mcu.

But these are not the best optimized ways. Can some-one guide me the best solution for this purpose along with schematic diagram.
I want the solution to use minimum components.

Thanks
 

Jahanzeb1

Newbie level 6
Joined
Mar 29, 2012
Messages
11
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,399
how about a current transformer? A hall effect sensor?
Thank you for replying. Yes well transformer and hall effect sensor can be used but transformer is bulky device and more over there are 8 bulbs and i want to know to status of each bulb separately n this means if i use transformer or hall effect sensor then i need 8 transformers/sensors for this purpose which will make the circuit too heavy and costly.

I want a very simple solution using a simple diode/zener diode if possible. I know that zener diode of 5v always drops 5v across itself when it is attached in series with load, so when AC voltage is applied on it it will drop 5v across itself and by using comparator i can determine the logic. Is it ok ?
 

barry

Advanced Member level 5
Joined
Mar 31, 2005
Messages
5,181
Helped
1,118
Reputation
2,248
Reaction score
1,123
Trophy points
1,393
Location
California, USA
Activity points
28,363
That doesn't sound good, because:
1) Your zener is going to have to carry all of the load current; you'll be dissipating 2.5 Watts in your poor zener for a 100W bulb, for example. You'll need a heatsink.
2) You're going to need either some isolation or a diff amp with a high-common mode rating.
3) Some other reasons I'm too lazy to go into.

How about a light detector?
 

amendar

Newbie level 6
Joined
Aug 6, 2013
Messages
13
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,351
How about sensing the current of load?!
 

betwixt

Super Moderator
Staff member
Joined
Jul 4, 2009
Messages
15,024
Helped
4,896
Reputation
9,812
Reaction score
4,696
Trophy points
1,393
Location
Aberdyfi, West Wales, UK
Activity points
127,671
How about an LDR and series resistor across the 5V supply, the connection between them will give you a logic level output depending on whether light was being emitted or not.

Brian.
 

Jahanzeb1

Newbie level 6
Joined
Mar 29, 2012
Messages
11
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,399

barry

Advanced Member level 5
Joined
Mar 31, 2005
Messages
5,181
Helped
1,118
Reputation
2,248
Reaction score
1,123
Trophy points
1,393
Location
California, USA
Activity points
28,363
Ok, so you've got an LED lit. What are you going to do with that? You've still got dangerous high voltage floating around. However, if that LED was the input of an optoisolator, you'd be fine.
 

FvM

Super Moderator
Staff member
Joined
Jan 22, 2008
Messages
48,519
Helped
14,272
Reputation
28,807
Reaction score
12,976
Trophy points
1,393
Location
Bochum, Germany
Activity points
280,610
I see the problem that a lamp short (can happen when the bulb burns out) will brobably burn the schottky diodes or the LED/optocoupler if no current limiting elements are added.

A current transformer (can be a small 6 or 10 mm core) would be still my favourite solution.
 

crutschow

Advanced Member level 5
Joined
Feb 22, 2012
Messages
3,881
Helped
922
Reputation
1,842
Reaction score
911
Trophy points
1,393
Location
Colorado USA Zulu -7
Activity points
21,929
How are you powering the micro-controller? Remember that everything will be not isolated from the mains if you don't use any isolator between your sense circuit and the micro-controller which creates a lethal shock hazard.
 

amendar

Newbie level 6
Joined
Aug 6, 2013
Messages
13
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
1,351
You can google search for " current transformer " known as CT.
 