Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Question about vfd voltage rating

Status
Not open for further replies.

Kajunbee

Advanced Member level 1
Joined
Nov 5, 2016
Messages
455
Helped
93
Reputation
186
Reaction score
105
Trophy points
1,323
Activity points
5,108
Is there any problem with running a 240 volt motor on a vfd rated for 480 volts.
 

VFD rating isn't the point, question is what's the actual input voltage the VFD is running from.

Generally, you need to set the VFD motor parameters accordingly. The motor insulation must be sufficient for the higher peak voltage, shouldn't be a problem with usual industrial motors. Motors can be often wired for higher (wye circuit) or lower (delta circuit) input voltage. It should surely use wye circuit if available.
 

    V

    Points: 2
    Helpful Answer Positive Rating
I only have access to 240 vac single phase. I was thinking maybe rectify it and feed to DC bus terminals.
 