Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

how to calculating capasitor 4 POWER FACTOR CORRECTION..

Status
Not open for further replies.

acus

Junior Member level 1
Joined
Sep 7, 2005
Messages
17
Helped
1
Reputation
2
Reaction score
0
Trophy points
1,281
Activity points
1,402
someone help... i need value of capasitor for power factor correction for powerline 1300 W
 

you need to calculate KVA by multiplying V and I,

Now you have KW and KVA->so you easily find KVAR from pithagoras low.

KVAR^2=KVA^2-KW^2.(^2=square).

Now, if KVAR=200,you need 200 var in capaciteve side for balance so you can calculate it by V*I*Xc=KVAR (Needed).

so your Xc=KVAR/V*I.
 

issrani_manoj said:
you need to calculate KVA by multiplying V and I,

Now you have KW and KVA->so you easily find KVAR from pithagoras low.

KVAR^2=KVA^2-KW^2.(^2=square).

Now, if KVAR=200,you need 200 var in capaciteve side for balance so you can calculate it by V*I*Xc=KVAR (Needed).

so your Xc=KVAR/V*I.

sorriii i'm so dumm please give some example...
 

See: "Practical power factor correction" ..

Chapter 11
POWER FACTOR
Power in resistive and reactive AC circuits
True, Reactive, and Apparent power
Calculating power factor
Practical power factor correction
Contributors
**broken link removed**

Regards,
IanP
 

IanP said:
See: "Practical power factor correction" ..

Chapter 11
POWER FACTOR
Power in resistive and reactive AC circuits
True, Reactive, and Apparent power
Calculating power factor
Practical power factor correction
Contributors
Regards,
IanP

thanks bro..!!! very usefull...
 