    16A 250V switch rated for 10000 ops at mains peak or zero cross?

    Hi,
    The below switch says its rated for 10000 operations. But does that mean 10000 operations with the switching happening at the zero crossings, or 10000 ops with switching happening at mains peak?

    I assume that the switching refers to when 16A flows at the instant of switch contact make?...ie not instances where in a 16A circuit, massive inrush of 70A (say) flows through the contacts at make time?

    Also, the datasheet says it doesn’t refer to inductive switching for the 10000 ops…but in reality , all circuits will have stray inductance, and so we can safely say that the real rating will be nowhere near 10000 ops?

    Do you agree that when this switch gets worn out...the contacts will stick together for some time instead of breaking immediately.?

    16A switch: (0911 on pg 172)
    https://www.infinite-electronic.hk/d...8350ABBB-B.pdf
    Last edited by treez; 5th January 2020 at 15:07.

    •   AltAdvertisement

        
       

  2. #2
    Super Moderator
    Points: 83,067, Level: 70
    Achievements:
    7 years registered
    Awards:
    2nd Helpful Member
    betwixt's Avatar
    Join Date
    Jul 2009
    Location
    Aberdyfi, West Wales, UK
    Posts
    13,658
    Helped
    4535 / 4535
    Points
    83,067
    Level
    70

    Re: 16A 250V switch rated for 10000 ops at mains peak or zero cross?

    You will have to ask them. They are "snap action" which usually means they have a spring activated mechanism and that in turn usually means they close and release very rapidly. All switches wear out eventually, I would guess their figures are not based on someone pressing the button 10,000 times in a variety of load situations but by wear on the mechanism and contacts from a smaller number of operations or by an automated pressing process.

    Brian.
    PLEASE - no friends requests or private emails, I simply don't have time to reply to them all.
    It's better to share your questions and answers on Edaboard so we can all benefit from each others experiences.


    1 members found this post helpful.

    •   AltAdvertisement

        
       

  3. #3
    Super Moderator
    Points: 264,236, Level: 100
    Awards:
    1st Helpful Member

    Join Date
    Jan 2008
    Location
    Bochum, Germany
    Posts
    46,168
    Helped
    14041 / 14041
    Points
    264,236
    Level
    100

    Re: 16A 250V switch rated for 10000 ops at mains peak or zero cross?

    all circuits will have stray inductance, and so we can safely say that the real rating will be nowhere near 10000 ops?
    A pointless statement, I think. There's a reason why switch and contactor rating distinguishes between resistive and inductive load, although any circuit has some inductance. An inductive load has L/R circuit time constant which is at least in the contact opening time order of magnitude, e.g. 100 us to several ms. That's not the case for a mostly resistive load.


    1 members found this post helpful.

    •   AltAdvertisement

        
       

  4. #4
    Advanced Member level 5
    Points: 34,294, Level: 45
    Achievements:
    7 years registered

    Join Date
    Sep 2008
    Location
    cambridge
    Posts
    7,122
    Helped
    516 / 516
    Points
    34,294
    Level
    45

    Re: 16A 250V switch rated for 10000 ops at mains peak or zero cross?

    Thanks, by "contact opening time" you are speaking of "contact bouncing time"?

    I believe we would agree that an ideal world resistive circuit, with no inductance, would not suffer any contact sparking as the switch bounced at make or break...thus the ideal resistive circuit, would last a very long time, as its the inductive sparking at make or break which does all the damage to switch contacts?



  5. #5
    Super Moderator
    Points: 81,102, Level: 69
    Achievements:
    7 years registered
    Awards:
    Most Frequent Poster 3rd Helpful Member

    Join Date
    Apr 2014
    Posts
    16,449
    Helped
    3731 / 3731
    Points
    81,102
    Level
    69

    Re: 16A 250V switch rated for 10000 ops at mains peak or zero cross?

    Hi,

    Imagine just the energy stored in the inductance.
    It creates the spark.
    Low energy will cause low damage, high energy will cause high damage.

    Klaus
    Please don´t contact me via PM, because there is no time to respond to them. No friend requests. Thank you.


    1 members found this post helpful.

  6. #6
    Advanced Member level 5
    Points: 34,294, Level: 45
    Achievements:
    7 years registered

    Join Date
    Sep 2008
    Location
    cambridge
    Posts
    7,122
    Helped
    516 / 516
    Points
    34,294
    Level
    45

    Re: 16A 250V switch rated for 10000 ops at mains peak or zero cross?

    i agree its low energy, though cant it spark off oxidation in the contacts? Also, the damage is cumulative, and the contact chrome coating is microscopically thin.
    Or would it be said that contact damage after xxx operations is due to the actual mechanical banging together of the contacts?...this is another low energy thing.
    I always thought it was the inductive sparking (made worse by bouncing), which damages contacts?



  7. #7
    Super Moderator
    Points: 264,236, Level: 100
    Awards:
    1st Helpful Member

    Join Date
    Jan 2008
    Location
    Bochum, Germany
    Posts
    46,168
    Helped
    14041 / 14041
    Points
    264,236
    Level
    100

    Re: 16A 250V switch rated for 10000 ops at mains peak or zero cross?

    There's typically no bouncing during contact opening.

    If the device has trustworthy specification, as I expect for a Bulgin product, and you don't have a dedicated inductive load, why not believe the spec? You didn't yet tell what the actual load is.


    1 members found this post helpful.

    •   AltAdvertisement

        
       

  8. #8
    Advanced Member level 5
    Points: 12,924, Level: 27

    Join Date
    Aug 2015
    Location
    Melbourne
    Posts
    2,118
    Helped
    773 / 773
    Points
    12,924
    Level
    27

    Re: 16A 250V switch rated for 10000 ops at mains peak or zero cross?

    all AC switches arc - obviously more for higher currents and higher L in series - if the contacts open quick enough ( quality AC switch ) then as soon as the current drops to zero, ( it does this 100/120 times per sec ) then that's it - open ckt - switch off ... where there is poor arc suppression - or if the plasma is allowed to exist near contacts that are too close together - you may get re-strike - this is the difference between a cheap AC switch and a good one ....



--[[ ]]--