    Converting pnp open drain transistor output to open collector for pule train

    hi there
    I have s7 1200 plc with pnp open drain transistor output to control Mitsubishi servo drive
    the drive sink input so how can I convert the signal

    •   AltAdvertisement

        
       

  2. #2
    Super Moderator
    Points: 74,732, Level: 66
    Achievements:
    7 years registered
    Awards:
    Most Frequent Poster 3rd Helpful Member

    Join Date
    Apr 2014
    Posts
    15,158
    Helped
    3448 / 3448
    Points
    74,732
    Level
    66

    Re: Converting pnp open drain transistor output to open collector for pule train

    Hi,

    I assume the PLC output is either
    * HIGH (what voltage?)
    * Z (high impedance)

    For low switching frequency you may simply connect a relay.

    For higher switching frequency I recommend to use a transistor.
    Now it depends on output logic what circuit to use.
    Tell us:
    PLC_High --> what output signal?
    PLC_Z --> what output signal?

    Tell us the input signal ranges of the Mitsubishi device:
    * for HIGH (voltage and current ranges)
    * for LOW (voltage and current ranges)

    Klaus
    Please donīt contact me via PM, because there is no time to respond to them. No friend requests. Thank you.



    •   AltAdvertisement

        
       

  3. #3
    Newbie level 2
    Points: 19, Level: 1

    Join Date
    Mar 2019
    Posts
    2
    Helped
    0 / 0
    Points
    19
    Level
    1

    Re: Converting pnp open drain transistor output to open collector for pule train

    hi,
    Tell us the input signal ranges of the Mitsubishi device:
    * for HIGH (voltage and current ranges)
    * for LOW (voltage and current ranges)
    the signal from plc 24v open drain transistor output 24v Dc

    one for the pulse and another output for the direction
    the input on the drive open collector (pp for the pulse input)
    (np for direction)
    vdd to 24 VDC
    sg to the ground
    plc siemens s71200
    servo drive mr j2s -A
    http://www.aiautomation.com.au/wp-co.../05/113788.pdf



    •   AltAdvertisement

        
       

  4. #4
    Super Moderator
    Points: 74,732, Level: 66
    Achievements:
    7 years registered
    Awards:
    Most Frequent Poster 3rd Helpful Member

    Join Date
    Apr 2014
    Posts
    15,158
    Helped
    3448 / 3448
    Points
    74,732
    Level
    66

    Re: Converting pnp open drain transistor output to open collector for pule train

    Hi,

    either one of us or you needs to read the datasheets ... I think it makes sense that you read it
    It shouldnīt be that difficult to find out input voltages and input currents.

    Sadly you donīt give the information if a PLC_HIGH should generate a Mitsubishi_HIGH or ..-LOW.

    Thus I tell the simple - inverting solution: HIGH --> LOW

    PLC_out -- 10k -- BJT1_base
    BJT1_base -- 1k -- GND
    BJT1_emitter -- GND
    BJT1_collector -- Mitsubishi_in


    In case the the Mitsubishi_input has no internal pullup --> you need an external pullup resistor:
    24V -- R_PU -- Mitsubishi_in

    BJT1 is a standard NPN transistor. In detail it depends on the (missing) voltage and currents. Try BC547
    R_PU value depends on Mitsubishi input voltages and currents. Try 10k, maybe you need a lower value.

    Klaus