    Experiment with electric ballast powered fluorescent tube

    I'm experimenting the tube light used in my house. I found the following results -
    Line voltage, Vl: 228.7 v
    Voltage across the ballast, Vb=172.7 v
    Voltage across the tube, Vt= 120.6 v

    All the voltages are measured in rms value. My question is why it is not satisfying the following?
    Vl=Vb+Vt

    Some more test results

    Current through the bulb and ballast, I= 0.339 A
    Measured power, P=41.6 w
    Power factor, pf=0.53

    Total power seems alright since it is a 36W tube light. I wanted to measure the power loss in the ballast due to heat and copper loss as well.

    •   AltAdvertisment

        
       

  2. #2
    Advanced Member level 5
    Points: 31,801, Level: 43
    Achievements:
    7 years registered

    Join Date
    Sep 2008
    Location
    cambridge
    Posts
    6,637
    Helped
    483 / 483
    Points
    31,801
    Level
    43

    Re: Experiment with electric ballast powered fluorescent tube

    All the voltages are measured in rms value. My question is why it is not satisfying the following?
    Vl=Vb+Vt
    that's an easy one for me to pick off for you...its because they are not in phase



  3. #3
    Super Moderator
    Points: 78,697, Level: 68
    Achievements:
    7 years registered
    Awards:
    2nd Helpful Member
    betwixt's Avatar
    Join Date
    Jul 2009
    Location
    Aberdyfi, West Wales, UK
    Posts
    12,885
    Helped
    4303 / 4303
    Points
    78,697
    Level
    68

    Re: Experiment with electric ballast powered fluorescent tube

    I suspect it may be a little more complicated than just the phase because each measurement is RMS across the respective component, phase would only enter the equation if one was relative to the other. The more likely reason is the waveform is different, the current through the tube is probably pulsed or non-linear as the voltage passes it's ignition threshold, the ballast drop would be approximately the incoming sine wave minus the pulsed tube current. Unless you take into consideration the different wave shapes when calculating RMS, the voltages would measure inaccurately.

    Brian.
    PLEASE - no friends requests or private emails, I simply don't have time to reply to them all.
    It's better to share your questions and answers on Edaboard so we can all benefit from each others experiences.



    •   AltAdvertisment

        
       

  4. #4
    Advanced Member level 5
    Points: 34,834, Level: 45
    Achievements:
    7 years registered Created Blog entry Created Album pictures
    SunnySkyguy's Avatar
    Join Date
    Sep 2007
    Location
    Richmond Hill, ON, Canada
    Posts
    6,705
    Helped
    1673 / 1673
    Points
    34,834
    Level
    45
    Blog Entries
    7

    Re: Experiment with electric ballast powered fluorescent tube

    I found the best way to tell if the ballast loss is by the temperature of the ballast. It ought to feel very slightly warm( 5'C above room) as if warmed by a 5W bulb or less.

    Is it the kind that all tubes fail if one fails?

    Then consider a modern ballast which is more efficient and has independent outputs. I used Quad 32W 4' tube ballasts which I can use for any number from 1 to 4 tubes. I choose tubes that compete with LEDs around 89 Lumens per Watt , tri-phosphor true daylight 5000'K with 85% CRI values. Tubes usually only come in bulk of 20 tubes and last 33k to 50k hrs.Fluorescent light effects compare to natural sun.pdf
    A good design question lists your overall requirements™ The best question deserves a better answer. ™
    ... Tony Stewart EE since 1975



  5. #5
    Super Moderator
    Points: 254,978, Level: 100
    Awards:
    1st Helpful Member

    Join Date
    Jan 2008
    Location
    Bochum, Germany
    Posts
    44,429
    Helped
    13528 / 13528
    Points
    254,978
    Level
    100

    Re: Experiment with electric ballast powered fluorescent tube

    To support betwixt's point, see below the voltage and current waveform of a 36W CFL operated with a conventional ballast.



    Treez is right nevertheless, the leading voltage phase of the inductive ballast is the primary reason why the voltages don't sum up as expected.

    A watt meter measuring ballast and current can determine the consumed real power (= losses).



  6. #6
    Advanced Member level 5
    Points: 12,423, Level: 26
    Achievements:
    7 years registered

    Join Date
    Apr 2010
    Posts
    1,889
    Helped
    405 / 405
    Points
    12,423
    Level
    26

    Re: Experiment with electric ballast powered fluorescent tube

    if the power measured is the power from mains , then loss in ballast is 5.6W.(all the readings are approximate. and assumption is flour. light is assumed to be 36W(which you have not measured))



  7. #7
    Advanced Member level 5
    Points: 14,458, Level: 29
    schmitt trigger's Avatar
    Join Date
    Apr 2013
    Posts
    2,406
    Helped
    783 / 783
    Points
    14,458
    Level
    29

    Re: Experiment with electric ballast powered fluorescent tube

    Is the ballast type old fashion? I mean by that, non-electronic, having only a transformer and capacitors?

    Because if it is an electronic ballast, the output will be a high frequency waveform. Not very many DMMs will be able to measure that.

    What instrument are you using to measure true power and power factor?
    My batteries are recharged by "Helpful Post" ratings.
    If you feel that I've helped you, please indicate it as a Helpful Post



    •   AltAdvertisment

        
       

  8. #8
    Advanced Member level 5
    Points: 34,834, Level: 45
    Achievements:
    7 years registered Created Blog entry Created Album pictures
    SunnySkyguy's Avatar
    Join Date
    Sep 2007
    Location
    Richmond Hill, ON, Canada
    Posts
    6,705
    Helped
    1673 / 1673
    Points
    34,834
    Level
    45
    Blog Entries
    7

    Re: Experiment with electric ballast powered fluorescent tube

    Quote Originally Posted by SunnySkyguy View Post
    I found the best way to tell if the ballast loss is by the temperature of the ballast. It ought to feel very slightly warm( 5'C above room) as if warmed by a 5W bulb or less. Does it?

    Is it the kind that all tubes fail if one fails?

    Then consider a modern ballast which is more efficient and has independent outputs. I used Quad 32W 4' tube ballasts which I can use for any number from 1 to 4 tubes. I choose tubes that compete with LEDs around 89 Lumens per Watt , tri-phosphor true daylight 5000'K with 85% CRI values. Tubes usually only come in bulk of 20 tubes and last 33k to 50k hrs.Fluorescent light effects compare to natural sun.pdf
    Pls answer
    A good design question lists your overall requirements™ The best question deserves a better answer. ™
    ... Tony Stewart EE since 1975



--[[ ]]--