Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Interesting PLC network problem

Status
Not open for further replies.

cruxader

Newbie level 5
Joined
Sep 13, 2003
Messages
10
Helped
0
Reputation
0
Reaction score
0
Trophy points
1,281
Activity points
148
plc subnet

We run a network of around 50 allen Bradley PLCs (SLC 5s) which are networked to control our facilities.

In the past fortnight between 9~13 of the PLCs mysteriously lost network connection at the same time (over 3 occasions). The error code was that the MAC suffered a hardware failure. Condition is recoverable but communications cannot resume.

In otherwords, must power cycle the affected PLCs.
The local agent and our facilities ppl are at their wits end. I have been asked to advice them

Any ideas?

What I have found so far:
1. Some sub-standard LAN cables have been identified and replaced. But there is no impact on the outage.
2. Failed PLCs are spread over more than 1 network hub/switches.
3. The PLCs network was connected to company intranet though it was isolated between 2nd and 3rd outage.
4. All but 1 of the affected PLCs had Network daughterboard version 2.19 (Version 2, Firmware Revision Number 19). The sole exception had 2.33. We have assortment of 2.19, 2.33, 2.40 & 2.50s. Not all 2.19s failed.
5. The PLCs are linked to half-dozen HMI PCs.
6. During the 2nd outage, the link between the PLC subnet & the company intranet went down too.
 

Status