Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Install 12VDc FAN into Uniterruptible Power Supply (UPS)

Status
Not open for further replies.

kengloong

Member level 4
Joined
Oct 15, 2005
Messages
68
Helped
2
Reputation
4
Reaction score
2
Trophy points
1,288
Location
Singapore
Activity points
1,966
Anyone can shown me how to install a 12VDc FAN into Uninterruptible Power Supply (UPS)? Is it I need to connect the FAN Positive Supply to the UPS Switch? Or some others else...

Hope to hear from you all soon.

Regards,
Keng Loong, Liew
 

sir

every UPSb had a battrey usualy 12 volt lead aced battrey so u could easlly conect
the fan terminals to the bat battry with resect to the polarty

regards
 

You can connect the 12-V fan to the battery terminal, but make sure that you connect only to 12-V not the whole battery because some UPS use series battery connection (to achieve more than 12V, e.g.: 24V or 48V).

And, don't forget to interconnect it to the UPS switch so that the fan will not run when you turn off the UPS.

aaNg
 

make sure that you connect only to 12-V not the whole battery because some UPS use series battery connection

This is a bad thing to do to a series stack of batterys. The batterys will not be charged equally and battery service life will be greatly reduced.

Anyone can shown me how to install a 12VDC FAN into Uninterruptible Power Supply (UPS)?

Wear safety glasses. Working on the inside of a big UPS is dangerous. 50V or more from a battery stack can hurt you even when the mains is off.

Do not wear a metal watch or finger rings. If your watch or ring shorts circuits the DC supply you will be badly burned.

The battery negative may be connected to earth. If you touch a soldering iron to battery DC with the mains cable connected, even with the mains switch off there can be a big bang.

If you short circuit somthing inside the UPS there can be smoke, fire and flying metal.

The correct answer is either
a) using your knowlege of electronics identify a suitable place where mains power is converted to 12V in the UPS

b)Get a suitable small mains to 12V power supply and put it inside the ups wired to the ups mains power.

or c) throw away the 12V fan and get a mains fan or a fan of a suitable voltage.
 