Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Transformer copper design

Status
Not open for further replies.

ismu

Full Member level 2
Joined
May 12, 2009
Messages
145
Helped
1
Reputation
2
Reaction score
1
Trophy points
1,298
Location
nil
Activity points
2,340
Hi

Assume I have 1kv transformer for 250v/4A input and out put is 100v;10A.
Can I load 50V/20A , here power rating is same.

If no , at what base transformer load has to given , power base or current base,?
If current base how can I select max rated current ?
 

Hi,

you don´t have a 1kV transformer --> you have a 1kVA transformer.

***
To your question:

Current:
If a transformer winding is rated for 10A, then you NEVER should draw 20A continous RMS current.
Maybe you could overload it for a short time...

Twice the RMS current will cause 4 times power dissipation and thus 4 times temperature rise.

***
Voltage: you say 50V:
How do you think you could get 50V from a 100V output?

Klaus
 
  • Like
Reactions: ismu

    ismu

    Points: 2
    Helpful Answer Positive Rating