Hi,
I am having actuator 240 V, that can take analog output of 4-20 mA signal.
Case 1, Fluke 4 to 20 mA battery operated 6V
it is very stable, no drifting
Case 2, A PLC 4 to 20 mA simulated by 24 V
It shows when the actuator go to the last position, it keep on drifting forward and backward
Current measure with Multi-meter shows consistent current reading. However the Voltage seems higher at 8 mA about 22 Volt.
Case 3, use another source using Potentiometer to generate 4-20 mA 24 V,
It is stable, no drifting
the voltage at 8 mA is 16 Volt.
We checked the mA using Fluke multimeter, all constant. What could be possible caused the drifting on case 2 .
I am having actuator 240 V, that can take analog output of 4-20 mA signal.
Case 1, Fluke 4 to 20 mA battery operated 6V
it is very stable, no drifting
Case 2, A PLC 4 to 20 mA simulated by 24 V
It shows when the actuator go to the last position, it keep on drifting forward and backward
Current measure with Multi-meter shows consistent current reading. However the Voltage seems higher at 8 mA about 22 Volt.
Case 3, use another source using Potentiometer to generate 4-20 mA 24 V,
It is stable, no drifting
the voltage at 8 mA is 16 Volt.
We checked the mA using Fluke multimeter, all constant. What could be possible caused the drifting on case 2 .