    Measuring leakage current in 3-phase system with current transformer

    Hi I want to measure precise number of leakage current in 3-phase trace heating system.
    The problem I faced is that typical current transformer gives a very high error at small currents. I found some solution either to use larger core or to apply some active compensation to pre-magnetize core.
    I think it is easier to pre-magnetize core because I have tight space requirements for the device, so larger core simply will not fit.
    But I can't find information about pre-magnetization. The only thing I know is I need to apply the voltage with same or 3 times frequency.
    In some industrial device, that does the same function I found two secondary windings, obviously one for pre-magnetization and one for measurement.

    Can somebody help me with this questions:

    1) What type of waveform do I need to apply to additional secondary winding?
    2) What parameters of additional secondary winding
    3) Can I use same core?

    Click image for larger version. 

Name:	808ecm13fig4.gif 
Views:	2 
Size:	10.4 KB 
ID:	134045

    •   Alt1st December 2016, 15:19

      advertising

        
       

  2. #2
    Super Moderator
    Points: 48,654, Level: 53
    Awards:
    Most Frequent Poster

    Join Date
    Apr 2014
    Posts
    9,970
    Helped
    2387 / 2387
    Points
    48,654
    Level
    53

    Re: Measuring leakage current in 3-phase system with current transformer

    Hi,

    a typical current transformer is for some Amperes, but I assume you only need to know about milliamperes.

    --> Because the usefull input current range is very low, you should use a couple of primary windings to get higher secondary signal.
    Maybe increase the burden resistor value.

    Klaus



    •   Alt1st December 2016, 16:17

      advertising

        
       

  3. #3
    Newbie level 2
    Points: 20, Level: 1

    Join Date
    Dec 2016
    Posts
    2
    Helped
    0 / 0
    Points
    20
    Level
    1

    Re: Measuring leakage current in 3-phase system with current transformer

    Quote Originally Posted by KlausST View Post
    Hi,

    a typical current transformer is for some Amperes, but I assume you only need to know about milliamperes.
    Yeah, something in range of 10-300 mA

    Quote Originally Posted by KlausST View Post
    --> Because the usefull input current range is very low, you should use a couple of primary windings to get higher secondary signal.
    Maybe increase the burden resistor value.
    Due to construction limitations, it is not possible to increase primary windings.
    And increasing burden resistor value doesn't help: insufficiently magnetized core has very poor current transfer performance :(



    •   Alt2nd December 2016, 12:55

      advertising

        
       

  4. #4
    Super Moderator
    Points: 234,575, Level: 100
    Awards:
    1st Helpful Member

    Join Date
    Jan 2008
    Location
    Bochum, Germany
    Posts
    40,534
    Helped
    12391 / 12391
    Points
    234,575
    Level
    100

    Re: Measuring leakage current in 3-phase system with current transformer

    Referring to you original question, a possible configuration to reduce errors by non-ideal core is a compensating feedback circuit that zeros the total flux.



  5. #5
    Advanced Member level 5
    Points: 13,005, Level: 27

    Join Date
    May 2015
    Location
    Melbourne, Australia
    Posts
    2,213
    Helped
    748 / 748
    Points
    13,005
    Level
    27

    Re: Measuring leakage current in 3-phase system with current transformer

    What kind of core material are you using ?
    Cheers, Tony.



--[[ ]]--