    why -48volt dc is used in telecommunications?

    why -48volt dc is used in telecommunication?

    •   Alt4th July 2016, 17:37

      advertising

        
       

  2. #2
    Super Moderator
    Points: 45,764, Level: 52

    Join Date
    Apr 2011
    Location
    Minneapolis, Minnesota, USA
    Posts
    11,422
    Helped
    2245 / 2245
    Points
    45,764
    Level
    52

    Re: why -48volt dc is used in telecommunications?

    Are you referring to telephone lines on land? In the US the live wire has a negative voltage, normally between -40 and -60 V. The reason is so that telephones can work during a blackout. The power comes from batteries at the telephone center. The high voltage can work for a long distance, because current is small.

    That's how it was years ago anyway. It's hard to be sure anymore, with fiber optics, cell towers, etc.

  3. #3
    Advanced Member level 5
    Points: 11,724, Level: 25

    Join Date
    Nov 2012
    Posts
    2,200
    Helped
    495 / 495
    Points
    11,724
    Level
    25

    Re: why -48volt dc is used in telecommunications?

    Quote Originally Posted by BradtheRad View Post
    The reason is so that telephones can work during a blackout. The power comes from batteries at the telephone center. The high voltage can work for a long distance, because current is small..
    I still do not understand - why the chosen voltage is negative? What is wrong with a positive voltage?

  4. #4
    Advanced Member level 3
    Points: 6,233, Level: 18
    Achievements:
    7 years registered

    Join Date
    Sep 2009
    Location
    Lancashire UK.
    Posts
    921
    Helped
    232 / 232
    Points
    6,233
    Level
    18

    Re: why -48volt dc is used in telecommunications?

    A little googling would answer this.

    http://electronics.stackexchange.com...stems-use-48-v
    http://archive.digivation.net/2006/0...ight-volts-dc/

    Basically to prevent corrosion. :)
    Before you ask - have you searched the forum? Have you searched Google? - Please do so.
    Please do not ask me in private - ask in public. Also please do not ask me to be a forum friend.
    If I have gone to the effort to help you etc then please have the decency to at least acknowledge it and do not just ask a question then never come back..

    •   Alt4th July 2016, 20:03

      advertising

        
       

  5. #5
    Advanced Member level 1
    Points: 3,005, Level: 12

    Join Date
    May 2012
    Posts
    433
    Helped
    97 / 97
    Points
    3,005
    Level
    12

    Re: why -48volt dc is used in telecommunications?

    -48V was chosen to prevent corrosion and is the highest voltage that can be used that will not pass a fatal level of current though the human heart.

  6. #6
    Advanced Member level 5
    Points: 13,005, Level: 27

    Join Date
    May 2015
    Location
    Melbourne, Australia
    Posts
    2,213
    Helped
    748 / 748
    Points
    13,005
    Level
    27

    Re: why -48volt dc is used in telecommunications?

    Quote Originally Posted by pjmelect View Post
    -48V was chosen to prevent corrosion and is the highest voltage that can be used that will not pass a fatal level of current though the human heart.
    This is the right answer.
    With a negative voltage {with respect to ground) any electrolytic action (ion migration) will be from the surroundings to the wire.

    In other words any resultant electroplating from leakage current will eat away the surroundings and deposit it on the wire, not eat away the wire.

    This is important where most of your wiring is either outside fully exposed to the weather, or buried in often very wet ground, and which may be expected to last for many tens of years without failure.
    Cheers, Tony.

    •   Alt5th July 2016, 00:56

      advertising

        
       

  7. #7
    Advanced Member level 5
    Points: 11,724, Level: 25

    Join Date
    Nov 2012
    Posts
    2,200
    Helped
    495 / 495
    Points
    11,724
    Level
    25

    Re: why -48volt dc is used in telecommunications?

    Quote Originally Posted by Warpspeed View Post
    This is the right answer.
    With a negative voltage {with respect to ground) any electrolytic action (ion migration) will be from the surroundings to the wire.
    Thanks; it sounds convincing. But telephone lines never use earth as the return path in any circuit. All telephone connections are minimum two wire devices and they will work even if you lift them from the ground. And this is true even at the exchange level, I believe.

  8. #8
    Advanced Member level 5
    Points: 13,005, Level: 27

    Join Date
    May 2015
    Location
    Melbourne, Australia
    Posts
    2,213
    Helped
    748 / 748
    Points
    13,005
    Level
    27

    Re: why -48volt dc is used in telecommunications?

    No they never do use a return path through the earth, it would be far too noisy.
    There is always a return wire associated with every signal wire.
    But one side of the system (positive side) is always at or very near ground potential.

    You simply cannot float all the buried communications wiring of hundreds of thousands of telephones in an entire city.
    Think about it....

    There will always be "some" electrical leakage down to ground practically everywhere.

    Its rather like the mains power distribution system, where the neutral wire is supposed to be at or near ground potential, and is actually deliberately grounded at many points around the entire system.
    Cheers, Tony.

  9. #9
    Advanced Member level 5
    Points: 11,724, Level: 25

    Join Date
    Nov 2012
    Posts
    2,200
    Helped
    495 / 495
    Points
    11,724
    Level
    25

    Re: why -48volt dc is used in telecommunications?

    Quote Originally Posted by Warpspeed View Post
    But one side of the system (positive side) is always at or very near ground potential.
    True; but then the corrosion argument falls flat; one wire will always be vulnerable to corrosion. Electrolysis will take place between the two wires and one of them will get eaten up, sooner or later.

  10. #10
    Advanced Member level 5
    Points: 13,005, Level: 27

    Join Date
    May 2015
    Location
    Melbourne, Australia
    Posts
    2,213
    Helped
    748 / 748
    Points
    13,005
    Level
    27

    Re: why -48volt dc is used in telecommunications?

    Yes that would certainly be true, if there is direct leakage between both wires.
    But in that case, your fully floating system would be no better off.

    Most dc systems use -ve as ground, its become the convention.

    But 50 volt dc based telecoms systems have always used positive ground because of the known corrosion problem.
    As an old telecoms trained technician, that is what we were taught.
    I can assure you that is the reason.
    Cheers, Tony.

--[[ ]]--