    APC UPS ES 500 back up battery doesnt work

    When I plug my ups apc es500 on the outlet it works perfectly fine but when a power outage occurs or if I unplug my UPS in the outlet my computer will turn off and a continous beeping sound occurs without the green light. I tested the battery using multimeter and it works perfectly fine the indicator shows 12volts to 13 volts.. Please help me with this problem. Thanks in advance

    •   Alt9th March 2016, 14:14

      advertising

        
       

  2. #2
    Super Moderator
    Points: 44,914, Level: 51

    Join Date
    Apr 2011
    Location
    Minneapolis, Minnesota, USA
    Posts
    11,133
    Helped
    2211 / 2211
    Points
    44,914
    Level
    51

    Re: APC UPS ES 500 back up battery doesnt work

    The batteries can read okay on a voltmeter but then lack the power to drive a load. They develop internal resistance, and this reduces how much Amperes they can put out.

    From my experience with a backup UPS, the batteries only last a few years (whether they are used much or little.) Then they must be replaced. Often they are gel cells. These are not made to have the lifetime of a deep cycle lead-acid battery.


    1 members found this post helpful.

    •   Alt9th March 2016, 19:42

      advertising

        
       

  3. #3
    Newbie level 2
    Points: 23, Level: 1

    Join Date
    Mar 2016
    Posts
    2
    Helped
    0 / 0
    Points
    23
    Level
    1

    Re: APC UPS ES 500 back up battery doesnt work

    Thank you for your quick response, so are you suggesting me to buy a new battery replacement in my UPS?? Does this solve my issue regarding my UPS? Thank you



    •   Alt10th March 2016, 08:42

      advertising

        
       

  4. #4
    Advanced Member level 5
    Points: 9,638, Level: 23

    Join Date
    Nov 2012
    Posts
    1,798
    Helped
    396 / 396
    Points
    9,638
    Level
    23

    Re: APC UPS ES 500 back up battery doesnt work

    Quote Originally Posted by BradtheRad View Post
    The batteries can read okay on a voltmeter but then lack the power to drive a load. They develop internal resistance, and this reduces how much Amperes they can put out.

    From my experience with a backup UPS, the batteries only last a few years (whether they are used much or little.) Then they must be replaced. Often they are gel cells. These are not made to have the lifetime of a deep cycle lead-acid battery.
    I call this a design feature. I believe all maintenance free lead acid batteries are gel cells. The capacity also decreases steadily (almost from the beginning) and they rarely last more than 2 years. The ones with external batteries last far longer (one is still alive and kicking after 4 years). I originally suspected that there are some faults in charging program but now I believe that I am wrong, as usual.


    1 members found this post helpful.