    3 phase power measurement with 1 wattmeter

    I want to measure the power KW of a motor that is Delta
    connected (3 wires, no neutral). I want to use only 1 watt-hour meter. The motor has balanced load but has harmonics because of an PWM invertor driving it at variable speed. (would it make any difference).

    Thanks for any suggestions.

  2. #2
    Full Member level 4
    Points: 3,419, Level: 13
    aNdreiBuuu's Avatar
    Join Date
    Apr 2001
    Location
    moon
    Posts
    225
    Helped
    23 / 23
    Points
    3,419
    Level
    13

    3 phase...

    U can use Atmel sollution (2 chips) for 3 phase powermeter.
    Search on atmel site,
    best,
    //a



  3. #3
    Full Member level 2
    Points: 3,857, Level: 14

    Join Date
    Feb 2002
    Location
    Sweden
    Posts
    120
    Helped
    0 / 0
    Points
    3,857
    Level
    14
    Provided the design of the driver is professional and the motor is of standard type I think it is safe to assume a symmetrical load.

    Regards



  4. #4
    Advanced Member level 3
    Points: 5,590, Level: 17

    Join Date
    Feb 2002
    Location
    Pakistan
    Posts
    839
    Helped
    57 / 57
    Points
    5,590
    Level
    17
    Thanks. But I want to ask the connections of the wattmeter with the 3 phase wires and the conversion factor to get the 3 phase power from 1 meter.



  5. #5
    Super Moderator
    Points: 37,750, Level: 47
    flatulent's Avatar
    Join Date
    Jul 2002
    Location
    Middle Earth
    Posts
    4,632
    Helped
    474 / 474
    Points
    37,750
    Level
    47

    artificial neutral

    How about making an artificial neutral point with a Y connected set of resistors which are much lower resistance than the voltage sense winding in your meter? This would solve the connection problem. I woul suspect, as one of the previous posts said, that the three phases are equal in current and power factor and therefore multiply one phase real power by three.



  6. #6
    Advanced Member level 3
    Points: 5,590, Level: 17

    Join Date
    Feb 2002
    Location
    Pakistan
    Posts
    839
    Helped
    57 / 57
    Points
    5,590
    Level
    17
    The @tmel solution looks very high-end. I intend to use An@log devices AD*775O which are very simple to use. Any suggestions on that.



  7. #7
    Advanced Member level 3
    Points: 5,590, Level: 17

    Join Date
    Feb 2002
    Location
    Pakistan
    Posts
    839
    Helped
    57 / 57
    Points
    5,590
    Level
    17
    flatulent, I remember reading a simpler arrangement in one our text books in EE. But that was in the last century and I have forgotten that.



  8. #8
    Super Moderator
    Points: 37,750, Level: 47
    flatulent's Avatar
    Join Date
    Jul 2002
    Location
    Middle Earth
    Posts
    4,632
    Helped
    474 / 474
    Points
    37,750
    Level
    47

    how about this

    How about conneting the voltage sense between two phases and the current in one line? Then calculate the equivalent line to neutral voltage with the square root of three factor. This should allow multiplying this one phase measurement by the square root of three to get the total power in three phases. Then as a final check, temporarily measure the power with two meters to verify the simpler method.



  9. #9
    Advanced Member level 3
    Points: 5,590, Level: 17

    Join Date
    Feb 2002
    Location
    Pakistan
    Posts
    839
    Helped
    57 / 57
    Points
    5,590
    Level
    17
    Does leaving the 3rd line free make any difference in your suggesion , flatulent



  10. #10
    Super Moderator
    Points: 37,750, Level: 47
    flatulent's Avatar
    Join Date
    Jul 2002
    Location
    Middle Earth
    Posts
    4,632
    Helped
    474 / 474
    Points
    37,750
    Level
    47

    I would think not

    I would think not. This and all other suggestions above rely on the lines being totally identical in current and power factor. As is usual in all prototyping situations, the comparason with a standard measurement method should be done at several motor loads to make sure some aspect was not over looked.

    I overlooked one point on the correction factor. The phase of the adjacent line will be different than the phase of the neutral.
    There may be some further correction factor of the reading. I am not in a position now to do the diagrams. But in general, the comparison with the two meter temporary measurement will give you the correction factor.



  11. #11
    Advanced Member level 3
    Points: 5,590, Level: 17

    Join Date
    Feb 2002
    Location
    Pakistan
    Posts
    839
    Helped
    57 / 57
    Points
    5,590
    Level
    17
    Someone has suggested that I just have to multiply the reading of the wattmeter by 2.0 and I will get the correct 3 phase power. No extra power factor corrections needed. I will try it out practically as you suggested. thnx



  12. #12
    sick_man
    Guest
    There is a simple way to measure watts consumed on each of the 3 phases.

    You need to multiply the reading from 1 phase {at no drive ie the controller is set to zero rotation}

    by pi 3.1457.

    To get the power factor of each phase
    simply then divide your outcome from above by 3

    To get each phases current

    do the same over several ranges of the controller

    then draw a graph ploting each point

    then divide each of these points numerical value by 3

    to get the watts on each phase

    this can be done over several phases then each can have its own colour

    the average plots {add the three phase reading divide by three}


    you then have a nice graph shows you how "symetrical" each phase actualy is

    not just a guess at it being symertical drive or not {they very seldom are unless you star point earth the whole system}


    the simple way to think of phase is a circle divided by three
    {if you dont use neutral {basicaly earth or the .1457 left over {this is the differance in potential {energy {reverse current not voltage} left over from three phases that make a circle}{take out of the equassion using earth
    same as neurtral}}

    neutral isnt a phase

    instead neutral is a kind of earth

    being just a long run earthed at the substation or power station that supplies your needs....

    so .1457 is all the potential {voltage but no foward current} that is can return to the genorator station or substation transformer

    lightning comes up from the ground 1.707 X less distance than it travels down.... this is a fact



  13. #13
    Super Moderator
    Points: 37,750, Level: 47
    flatulent's Avatar
    Join Date
    Jul 2002
    Location
    Middle Earth
    Posts
    4,632
    Helped
    474 / 474
    Points
    37,750
    Level
    47

    calculatins

    I agree with the 2.0 factor for two reasons.

    1) I did the calculations at lunch and it shows 2.0

    2) A thought experiment with the two meter method shows equal readings for the equal phase loads. Summing the two meter readings will result in twice the reading for one meter.



  14. #14
    Advanced Member level 3
    Points: 5,590, Level: 17

    Join Date
    Feb 2002
    Location
    Pakistan
    Posts
    839
    Helped
    57 / 57
    Points
    5,590
    Level
    17
    Thanks flatulent. I think it solves the problem then