    2 transformers in parallel?

    Is is possible to wire (2 of the same part number) 20A, 18V step-down transformers to increase load handling?
    They are center tap transformers, but the intention would be not to tap them at the center but rather both at the 18V secondary taps.
    If it is possible are there any precautions?
    Last edited by cgchas; 23rd October 2011 at 05:05.

    •   Alt23rd October 2011, 04:44

      advertising

        
       

  2. #2
    Member level 5
    Points: 1,742, Level: 9

    Join Date
    Mar 2010
    Location
    mashhad
    Posts
    86
    Helped
    26 / 26
    Points
    1,742
    Level
    9

    Re: 2 transformers in parallel?

    if they are same its possible. you should connect one end of each outputs together and measure the voltage at two remaining ends. if the measured voltage (AC voltage) is near to 0V, you can connect two remaining ends together also. and if the measured voltage is about twice the output voltage, then you should swap first connections.
    in general, when one end of each outputs connected to each other, the AC voltage between remaining ends should be about 0V. at this situation you can safely connect remaining ends.s.JPG


    2 members found this post helpful.

    •   Alt23rd October 2011, 05:51

      advertising

        
       

  3. #3
    Member level 2
    Points: 852, Level: 6

    Join Date
    Jul 2011
    Posts
    51
    Helped
    4 / 4
    Points
    852
    Level
    6

    Re: 2 transformers in parallel?

    Quote Originally Posted by hamed8419215 View Post
    if they are same its possible. you should connect one end of each outputs together and measure the voltage at two remaining ends. if the measured voltage (AC voltage) is near to 0V, you can connect two remaining ends together also. and if the measured voltage is about twice the output voltage, then you should swap first connections.
    in general, when one end of each outputs connected to each other, the AC voltage between remaining ends should be about 0V. at this situation you can safely connect remaining ends.s.JPG
    Thank you.

    I wonder. Are there issues with doing this with benchtop power supplies? If both are set to the same voltage, can their grounds be connected and both positive outputs be tapped (in parallel) to split the load between the two?


    1 members found this post helpful.

    •   Alt23rd October 2011, 07:25

      advertising

        
       

  4. #4
    FvM
    FvM is offline
    Super Moderator
    Points: 170,895, Level: 98
    Awards:
    1st Helpful Member

    Join Date
    Jan 2008
    Location
    Bochum, Germany
    Posts
    27,175
    Helped
    8421 / 8421
    Points
    170,895
    Level
    98

    Re: 2 transformers in parallel?

    DC power supplies can be generally connected in parallel. But depending on their characteristic, a stable and equal load share may not be achieved due to there low internal resistance. You achieve the best results with individual cables connecting the point of load.

    Transformers have an internal impedance that helps to share the load current. But besides having equal open circuit voltage (respectively windings ratio), the internal impedance must be also equal for transformers of equal nominal power, otherwise the transformer with the lower impedance will be overloaded. Under this condition, paralleling of transformers is common practice in power distribution systems. Of course it also work on a lab bench. Using transformers of the same type is the most obvious way to meet the said condition. But it also works for transformers of different size, if they have equal impedance voltage respectively rated percent impedance.


    1 members found this post helpful.

  5. #5
    Advanced Member level 2
    Points: 5,127, Level: 16

    Join Date
    Jan 2007
    Location
    Sweden
    Posts
    565
    Helped
    251 / 251
    Points
    5,127
    Level
    16

    Re: 2 transformers in parallel?

    For parallel transformers, do not place them too close to each other as it can increase heat and losses. Even if both have same characteristic is it a good idea with a fuse for each winding. If one winding becomes shortcut gives fuses a chance that at least one transformer survive.
    Even better protection is to let each winding have its own rectifying bridge before they are connected in parallel.