    impedance of a solenoid

    Did some searching of the forum, but didn't find an answer to my question.

    If you used an ohm meter, and measured across a solenoid coil are you measuring the resistance of the coil or the reactance?

    What I want to do is calculate the inrush and holding currents of a solenoid valve in a 24V AC 60 Hz application.

    So if I take a measurement of the solenoid coil with the plunger in the open position and the closed position would I use this ohms value to calculate the inrush and holding current with ohms law? I'm currently reading 23Ω in the open position. Which should equal 1.04 Amp but the manufacturer rates the inrush at 0.41 Amp.

    If not is there a way to calculate the inrush current and how do I do it? Also is there any possible way that the inrush current could be made larger. (Other than pulling the solenoid plunger further out of its open resting position) Say something like the plunger having a greater amount of pull, or a lower than 24 voltage applied to it. Or is the inrush current for a specific coil set by the resistance and just the amount of time the inrush current would be present before lowering to the holding current would be changed by these things such as voltage and pull.

    Thanks for any help you can provide.

    •   Alt12th January 2009, 15:23

      advertising

        
       

  2. #2
    FvM
    FvM is offline
    Advanced Member level 5
    Points: 167,965, Level: 97
    Awards:
    Helpful gold

    Join Date
    Jan 2008
    Location
    Bochum, Germany
    Posts
    26,598
    Helped
    8246 / 8246
    Points
    167,965
    Level
    97

    coil inrush resistance/reactance

    You can't measure the AC impedance of a solenoid valve with an ohmmeter. For an exact measurement, you should use a shunt or current probe and an oscilloscope. But usually, manufacturers specify inrush and holding current and holding power consumption. So there is to need for measurements.



    •   Alt12th January 2009, 18:14

      advertising

        
       

  3. #3
    Advanced Member level 5
    Points: 34,412, Level: 45
    Audioguru's Avatar
    Join Date
    Jan 2008
    Location
    Toronto area of Canada
    Posts
    4,049
    Helped
    829 / 829
    Points
    34,412
    Level
    45

    acceptable solenoid valve coil resistance

    The current into an inductor rises slowly. A solenoid is an inductor. There is no "inrush" current like there is into a capacitor.



    •   Alt13th January 2009, 02:35

      advertising

        
       

  4. #4
    Banned
    Points: 8,931, Level: 22

    Join Date
    Jan 2007
    Posts
    943
    Helped
    176 / 176
    Points
    8,931
    Level
    22

    amperage measurement coils

    Hi,
    I am also not clear about the term inrush current, unless due to activation of the plunger, the effective inductance increases.
    Any how, you can measure the Operate and release current by applying a variable AC voltage source in series with an AC current meter to the solenoid. For AC coils it is the inductance that matters more than the DC resistance that you measure with an Ohm meter. The resistance gets added vectorially to the AC reactance of the inductance.

    By the way, why do you want to increase the inrush current ? Obviously if the plunger is moved away, you need more force and therefore more current to operate it.

    Regards,
    Last edited by keith1200rs; 16th October 2013 at 08:50. Reason: Advertising removed



  5. #5
    FvM
    FvM is offline
    Advanced Member level 5
    Points: 167,965, Level: 97
    Awards:
    Helpful gold

    Join Date
    Jan 2008
    Location
    Bochum, Germany
    Posts
    26,598
    Helped
    8246 / 8246
    Points
    167,965
    Level
    97

    solenoid coil measurements

    To understand the usual solenoid valve terminology, you have to know a bit about the specific properties of AC operated valves. As the first point, inrush is the usual term for the higher turn-on current of AC solenoid valves, found in any datasheet.

    It happens, cause the inductance of the solenoid is considerably lower in off state. When the coil is energized, the plunger moves and closes the magnetic path. The effect is utilized to get a faster and more powerfull action with higher initial current and lower static power consumption. It's an inherent advantage of AC solenoids (the same with AC driven contactors BTW, this should be rather known by interested engineers).



  6. #6
    Advanced Member level 5
    Points: 34,412, Level: 45
    Audioguru's Avatar
    Join Date
    Jan 2008
    Location
    Toronto area of Canada
    Posts
    4,049
    Helped
    829 / 829
    Points
    34,412
    Level
    45

    how to measure induction of a coil

    Yes, of course. The plunger is the core of the inductor and the inductance changes as the plunger moves.
    So there is a useful inrush higher current.