Welcome to our site! EDAboard.com is an international Electronics Discussion Forum focused on EDA software, circuits, schematics, books, theory, papers, asic, pld, 8051, DSP, Network, RF, Analog Design, PCB, Service Manuals... and a whole lot more! To participate you need to register. Registration is free. Click here to register now.

Level Measurement DP type problem

Status
Not open for further replies.

cheetha

Full Member level 2
Joined
Sep 17, 2011
Messages
146
Helped
1
Reputation
2
Reaction score
2
Trophy points
1,298
Activity points
2,310
Hi,
We are using diaphragm type Differential Pressure transmitters for level measurement of different vessels. Each vessel consists of two transmitters one with PLC loop (HIMA with current isolator card CS4/420) {let name it A} and other with DCS loop {let name it B}. The transmitter A show erratic behavior while transmitter B is relatively stable.
• Both transmitters are of identical model and make and have exact same configuration & installed at same vessel and diaphragms are located at adjacent locations,
• The grounding connections were found ok.
• When transmitter A is forced to any value the trend behaves normal and sets to a fix value
• The transmitter A was replaced with new one but behavior didn’t changed.
what could have caused transmitter to behave erratically.

Thanks in advance
 

Hi,

transmitter A show erratic behavior
This is no error description, therefore we can not use it to solve the problem.

• When transmitter A is forced to any value the trend behaves normal and sets to a fix value
Isn't this correct behaviour?
If not, describe what you expect...and what is not like expected.

Klaus
 

Hello,

1. Interchange the connections of the two transmitters. If the problem shifts to transmitter B, then probably the problem is with PLC or related wiring. If the problem stays with transmitter A, then probably the problem is in the installation of the transmitter A.

2. For liquid level measurement with DP transmitter, usually dry/wet reference leg installation methods are used. See the picture (dry reference leg) below.



You can see a drain valve. Your system must have such a drain/fill valve (solenoid/pneumatic etc.) which will be controlled from PLC/DCS. Does that valve work properly?
 

Hi,

This is no error description, therefore we can not use it to solve the problem.

Klaus

The erratic behavior means the output is undesirable and unpredictable. Please find attached images

**broken link removed**
**broken link removed**
**broken link removed**
**broken link removed**


Hi,

• When transmitter A is forced to any value the trend behaves normal and sets to a fix value
Isn't this correct behaviour?
If not, describe what you expect...and what is not like expected.

Klaus

when transmitter is forced to a fixed value it behaves normally as required, this ensures there is no problem in the loop. Please find the attached images.


**broken link removed****broken link removed****broken link removed**


in images the green colored is tx B where as blue colored is tx A

- - - Updated - - -

1. Interchange the connections of the two transmitters. If the problem shifts to transmitter B, then probably the problem is with PLC or related wiring. If the problem stays with transmitter A, then probably the problem is in the installation of the transmitter A.

Actually the truth is if one is transmitter is working properly and other transmitter is showing Ghost behavior, therefore there is a risk of going completely blind. the transmitter A is replaced with new one but still the problem persists.


2. For liquid level measurement with DP transmitter, usually dry/wet reference leg installation methods are used.
You can see a drain valve. Your system must have such a drain/fill valve (solenoid/pneumatic etc.) which will be controlled from PLC/DCS. Does that valve work properly?

we are using diaphragm type for that capillary tube is attached with filled liquid, this maxes it wet leg and completely isolated/sealed.

Thanks
 

Measure the output current (4-20 mA) of the transmitter.
During unstable behavior is the output current stable ?

Is the unstable behavior is related with any noise source ?
(for example, the problem may starts when a VFD controlled motor is started)

Unfortunately the attachments in post #4 can't be seen.
 

Hunting 2.pngHunting while in process 1.pngHunting while in process.pngLoop Checking by forcing TX at Fix value (2).pngLoop Checking by forcing TX at Fix value.pngLoop Checking with External mA Source.png

- - - Updated - - -

Measure the output current (4-20 mA) of the transmitter.
During unstable behavior is the output current stable ?

Is the unstable behavior is related with any noise source ?
(for example, the problem may starts when a VFD controlled motor is started)

The current is unstable, it also fluctuates.
The problem persists indefinitely irrespective to any plant conditions.
if there was noise problem then the value should have fluctuated when in forced condition.(i think)

thanks
 

Is there any external power supply (e.g 24VDC) which is supplying current to all the sensors ? See the picture below.



You can see a power supply unit. Old SMPS power supply unit may give high ripples (Due to old electrolytic capacitors) at its output and may cause trouble. If there is a common power supply unit, check its output using oscilloscope.

How do you make a force condition ? Do the transmitters have display and keypad ?

If possible upload the datasheet of transmitter and wiring diagram which shows how the transmitter, PLC card etc are connected with each other.
 

Hi,
apologies for late replying.
the transmitter is loop powered no seperate/ external power supply.
forcing is accomplished by using HART, yes tx has display
 
Last edited: