    Level Measurement DP type problem
    We are using diaphragm type Differential Pressure transmitters for level measurement of different vessels. Each vessel consists of two transmitters one with PLC loop (HIMA with current isolator card CS4/420) {let name it A} and other with DCS loop {let name it B}. The transmitter A show erratic behavior while transmitter B is relatively stable.
    • Both transmitters are of identical model and make and have exact same configuration & installed at same vessel and diaphragms are located at adjacent locations,
    • The grounding connections were found ok.
    • When transmitter A is forced to any value the trend behaves normal and sets to a fix value
    • The transmitter A was replaced with new one but behavior didn’t changed.
    what could have caused transmitter to behave erratically.
    Thanks in advance
    •   Alt20th December 2016, 07:08
      advertising
  2. #2
    Super Moderator
    Points: 57,561, Level: 58
    Achievements:
    7 years registered
    Awards:
    Most Frequent Poster 3rd Helpful Member
    Join Date
    Apr 2014
    Posts
    11,719
    Points
    57,561
    Level
    58
    Re: Level Measurement DP type problem
    This is no error description, therefore we can not use it to solve the problem.
    Isn't this correct behaviour?
    If not, describe what you expect...and what is not like expected.
    Klaus
  3. #3
    Full Member level 5
    Points: 2,497, Level: 11
    Join Date
    May 2012
    Bangladesh
    Posts
    290
    Points
    2,497
    Level
    11
    Hello,
    1. Interchange the connections of the two transmitters. If the problem shifts to transmitter B, then probably the problem is with PLC or related wiring. If the problem stays with transmitter A, then probably the problem is in the installation of the transmitter A.
    2. For liquid level measurement with DP transmitter, usually dry/wet reference leg installation methods are used. See the picture (dry reference leg) below.
    You can see a drain valve. Your system must have such a drain/fill valve (solenoid/pneumatic etc.) which will be controlled from PLC/DCS. Does that valve work properly?
    •   Alt20th December 2016, 08:22
      advertising
  4. #4
    Full Member level 2
    Join Date
    Sep 2011
    Posts
    146
    Points
    1,563
    Level
    9
    Quote Originally Posted by KlausST View Post
    Klaus
    The erratic behavior means the output is undesirable and unpredictable. Please find attached images
    Attachment 134704
    Attachment 134705
    Attachment 134706
    Attachment 134707
    Klaus
    when transmitter is forced to a fixed value it behaves normally as required, this ensures there is no problem in the loop. Please find the attached images.
    Attachment 134708Attachment 134709Attachment 134710
    in images the green colored is tx B where as blue colored is tx A
    Quote Originally Posted by ahsan_i_h View Post
    Actually the truth is if one is transmitter is working properly and other transmitter is showing Ghost behavior, therefore there is a risk of going completely blind. the transmitter A is replaced with new one but still the problem persists.
    we are using diaphragm type for that capillary tube is attached with filled liquid, this maxes it wet leg and completely isolated/sealed.
    Thanks
    •   Alt21st December 2016, 08:00
      advertising
  5. #5
    Full Member level 5
    Join Date
    May 2012
    Bangladesh
    Posts
    290
    Points
    2,497
    Level
    11
    Measure the output current (4-20 mA) of the transmitter.
    During unstable behavior is the output current stable ?
    Is the unstable behavior is related with any noise source ?
    (for example, the problem may starts when a VFD controlled motor is started)
    Unfortunately the attachments in post #4 can't be seen.
  6. #6
    Full Member level 2
    Join Date
    Sep 2011
    Posts
    146
    Points
    1,563
    Level
    9
    Click image for larger version.
ID:	134745Click image for larger version.
Name:	Hunting while in process 1.png
ID:	134746Click image for larger version.
Name:	Hunting while in process.png
ID:	134747Click image for larger version.
Name:	Loop Checking by forcing TX at Fix value (2).png
ID:	134748Click image for larger version.
Name:	Loop Checking by forcing TX at Fix value.png
ID:	134749Click image for larger version.
Name:	Loop Checking with External mA Source.png
    The current is unstable, it also fluctuates.
    The problem persists indefinitely irrespective to any plant conditions.
    if there was noise problem then the value should have fluctuated when in forced condition.(i think)
    thanks
  7. #7
    Full Member level 5
    Join Date
    May 2012
    Bangladesh
    Posts
    290
    Points
    2,497
    Level
    11
    Is there any external power supply (e.g 24VDC) which is supplying current to all the sensors ? See the picture below.
    You can see a power supply unit. Old SMPS power supply unit may give high ripples (Due to old electrolytic capacitors) at its output and may cause trouble. If there is a common power supply unit, check its output using oscilloscope.
    How do you make a force condition ? Do the transmitters have display and keypad ?
    If possible upload the datasheet of transmitter and wiring diagram which shows how the transmitter, PLC card etc are connected with each other.
    •   Alt23rd December 2016, 10:41
      advertising
  8. #8
    Full Member level 2
    Join Date
    Sep 2011
    Posts
    146
    Points
    1,563
    Level
    9
    apologies for late replying.
    the transmitter is loop powered no seperate/ external power supply.
    forcing is accomplished by using HART, yes tx has display
  9. #9
    Full Member level 2
    Join Date
    Sep 2011
    Posts
    146
    Points
    1,563
    Level
    9
    please find datasheet
    http://obrazki.elektroda.pl/2004730900_1483773204.png